Rectangular panel inside a false work, Civil Engineering

Assignment Help:

Question
In erection of false work, for a rectangular panel inside a false work would it be braced all along two diagonals?

Answer
While a rectangular panel is focus to the eccentric load or the lateral load, it tends to distort into a parallelogram with one diagonal shortening and other elongating.

Supposedly, it is enough to brace along one of diagonals if one diagonal is only allowed to brace inside the rectangular panel, it must be not braced in diagonal in compression as under severe lateral loading diagonal might buckle leading to failure of structure.

But, in actual situation lateral loads could come from both sides of panel and therefore it should be there braced in both diagonals.

 


Related Discussions:- Rectangular panel inside a false work

Maintenance of terminal building, Maintenance of Terminal Building: A...

Maintenance of Terminal Building: All accessories such as lighting, water, sanitation, telephone and public address system should be maintained in a good condition. Disposal

Determine the meaning of relaxation of steel, Determine the meaning of Rela...

Determine the meaning of Relaxation of Steel If the strain in steel is kept constant, it is seen that stresses in it reduce with time. It is called as relaxation of steel. Ten

Principle of airlifting for cleaning pile bores, Q. Principle of airlifting...

Q. Principle of airlifting for cleaning pile bores? Airlifting is generally carried out before concreting to remove debris and clean the base of pile bores. It basically acts a

Surveying, if bearing of AB is 190& that of CB is 260,the included angle AB...

if bearing of AB is 190& that of CB is 260,the included angle ABC is how?

Define the term - clamp splice, Define the term - Clamp splice In a Cla...

Define the term - Clamp splice In a Clamp splice, bolts and nuts alongwith clamp plates are used. Tendons are held in-between the clamp plates and these clamp plates are tighte

Concrete technology, why strength of transition zone is less than bulk past...

why strength of transition zone is less than bulk paste

Fore bearing, find out the interior angleS with diagrame LINE AB, BC, CD, D...

find out the interior angleS with diagrame LINE AB, BC, CD, DE, EA Fore bearing 60''30" , 122'' , 46'' , 205''30" , 300''

Calculate the annual cost of alum - coagulation, Incoming water contains 2....

Incoming water contains 2.5 mg/L as a substance of natural alkalinity (HCO 3 - ). The flow rate is 9.5 ML/day). (a) What feed rate is required if the alum dose is 7 mg/L and

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd