Total volume of soil that excavated from the borrow area, Civil Engineering

Assignment Help:

Project specifications require a relative compaction of 95% (modified Proctor).  Construction of a highway embankment requires 10,000-yd3 of fill.  The borrow soil has an in-situ dry density of 94-PCF and a laboratory maximum dry density of 122.5-PCF.  The total volume of soil that must be excavated from the borrow area is most nearly:

Solution: The most common method of assessing the quality of field compaction is to calculate the Relative Compaction (RC) of the fill, defined as:

RC = 100 * (field dry density, PCF) / Laboratory maximum dry density (PCF)

Apply the equation using the given data:   

RC = 100 x 94-PCF / 122.5-PCF = 76.73%

Calculate the required volume of soil that must be excavated from the borrow area:  

(Required Fill) x (Compaction %) x (Relative Compaction)-1 = Excavated   Volume (borrow)

 10,000-yd3 of fill x (95%) x (76.73%)-1 = 12,380-yd3

 


Related Discussions:- Total volume of soil that excavated from the borrow area

Example of magnetic dip, Example : Line AB was drawn with a magnetic ...

Example : Line AB was drawn with a magnetic bearing of 136° 45′ while the magnetic declination was 2° 30′ east In an old map. If magnetic declination is 3° 30′ west to what m

Define lead lag relationships - construction management, Define Lead Lag Re...

Define Lead Lag Relationships 1. A lead is when the successor task begins before the predecessor task is complete 2. A lag is when a successor task does not

Compacted thickness of bituminous pavement, Q. Compacted thickness of bitum...

Q. Compacted thickness of bituminous pavement? The choice of compacted thickness is closely related to the nominal maximum size of aggregates of bituminous materials. Based on

Remedial measures for problems in turbid water - reflection, Remedial measu...

Remedial measures for Problems in Turbid Water - Reflection? The problem of reflection can be minimised by carefully placing the flash away from the axis of the camera and at a

Design the 2-span continuous center, Design the 2-span continuous center T-...

Design the 2-span continuous center T-beam, B2, for the floor syetem shown below. The girders that the beam frames into are all 24" wide. Using fc'= 5 ksi, and fy = 60 ksi. The ser

Key role of drilling fluid in rotary drilling, Question What is key rol...

Question What is key role of drilling fluid in rotary drilling in site search? Answer Drill fluid in rotating serves two main reasons. (i) Facilitate rotation of

Hydrometer analysis - soil mechanics and foundations, Hydrometer Analysis -...

Hydrometer Analysis - soil mechanics and foundations Hydrometer Analysis used to obtain the grain size distribution of fine-grained soils (finer sands, silts and clays) smalle

Closing and opening of expansion joints and contraction join, Question ...

Question In case of for unreinforced concrete carriageway, what will succession of closing and opening of expansion joints and contraction joints? Answer Take a case t

What is the correct value of the specific gravity, In a specific gravity te...

In a specific gravity test, 1.17 N of oven-dired soil was taken. The weight of pyknometer, soil and water was obtained as 6.51 N. The weight of pyknometer full of water alone was 5

Stacking of materials for building, briefly explain the stacking of materia...

briefly explain the stacking of materials in the site for general building

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd