Increasing concrete cover beyond contractual, Civil Engineering

Assignment Help:

Question
If contractor suggests increasing concrete cover beyond contractual such as 40mm to 70mm shall engineers accept suggestion?

Answer
In contractual part, based on requirement of General Specification of Civil Engineering Works, tolerance of concrete cover is involving +5mm and -5mm and engineers must not believe sub-standard work as they do not possess an authority to change acceptance criteria. In that case where engineers think contractor suggestion acceptable in technical point of view, consent has to be required from employer regarding changes in receiving criteria.

From practical point of view, effect on cracking because of an enlarge in concrete cover have to be considered. In general, there are three major parameters which govern crack width, namely tensile damage at the point considered, distance of longitudinal bar to concerned point and depth of tension zone.

For second factor, as in proximity of longitudinal bars to point of part, closer a bar is to this point; smaller is crack width. So, closely spaced bars with smaller cover determination give narrower cracks than extensively spaced bars with larger cover. So, with an increase of concrete cover, crack width will add to that is undesirable.

 


Related Discussions:- Increasing concrete cover beyond contractual

Equllibrium, how to know about he sign convention for equllibrium forces

how to know about he sign convention for equllibrium forces

Concrete structure be entirely free of expansion joints, Question Would a c...

Question Would a concrete structure be entirely free of expansion joints and contraction ? Answer Consider that concrete structure is not subject to problem of disparity settlem

Engg surveying, what does mean by too short and too long in erroneous tape ...

what does mean by too short and too long in erroneous tape length?

Designing of access ramps for drainage channels, Question Designing of ...

Question Designing of access ramps for drainage channels, why must direction of access ramps is sloping down on the way to downstream ? Answer In designing of access

Stainless steel really stainless in construction purpose, Question Is i...

Question Is it true that stainless steel really stainless in construction purpose ? Answer Stainless steel refers to alloy steels with more than 10.5 percent of chrom

Water absorption test for precast concrete pipes, Question What is the ...

Question What is the major purpose of carrying out water absorption test for precast concrete pipes? Answer Cement will mix with additional water than is compulsory t

Transportatoin engineening, explain the construction while aligning roads o...

explain the construction while aligning roads on hilly areas

Calculate the uniformly distributed load, Given: pretensioned rectangula...

Given: pretensioned rectangular beam b=6" h=20" f'c=4000psi f'ci=3000psi fti=.165ksi fts=.38ksi fci=1.8ksi fcs=1.8ksi R=0.80 Required: (a)Pi and e to maximize Md+

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd