Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

A synchronous motor with a synchronous reactance , A synchronous motor with...

A synchronous motor with a synchronous reactance of 12 ohms is operating with a current of 100 A at unity power factor supplying power to a large compressor. The phasor diagram for

Explain the different coupling schemes used in amplifiers, Q. Explain the d...

Q. Explain the different coupling schemes used in amplifiers? When amplifiers are cascaded, it is necessary to use a coupling network between the output of one amplifier and th

Determine potential difference across resistor, Determine Potential Differe...

Determine Potential Difference: Compute the current through each element of the given network and also determine potential difference across 15 Ω resistor. Figure

Power diode - power semiconductor devices , Power Diode A power diode i...

Power Diode A power diode is a two terminal, anode a and cathode K and  two layer P  and  N  junction devices. A PN  junction normally  formed  by allowing  diffusion and epita

Function of circuit - breaker, Q. Function of circuit - breaker, difference...

Q. Function of circuit - breaker, difference between circuit breaker and 'isolator'? Ans: The function of circuit breaker is to break the electrical continuity in the event o

Define some applications of digital counters, Define some Applications of D...

Define some Applications of Digital Counters? Digital counters are extremely useful in many applications. They can be effortlessly found in digital clocks and parallel-to-seri

Determine the transformer winding currents, Q. Three single-phase 100-kVA, ...

Q. Three single-phase 100-kVA, 2400:240-V, 60-Hz transformers (each ofwhich has an equivalent series impedance of 0.045+j0.16 referred to its low-voltage side) are connected to fo

Explain input characteristic of common emitter configuration, Q. Explain Th...

Q. Explain The Input Characteristics Of Common Emitter Configuration? Input characteristics:In the figure the abscissa is the base current IB, The ordinate is the base to emitter

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd