Explain balanced wye-connected load, Electrical Engineering

Assignment Help:

Balanced Wye-Connected Load

Let us consider a three-phase, four-wire 208-V supply system connected to a balanced wye connected load with an impedance of 10 20° , as shown in Figure (a). We shall solve for the line currents and draw the corresponding phasor diagram.

Conventionally it is assumed that 208 V is the rms value of the line-to-line voltage of the supply system, and the phase sequence is positive, or A-B-C, unless mentioned otherwise. The magnitude of the line-to-neutral (or phase) voltages is given by 208/√3, or 120 V. Selecting the line currents returning through the neutral conductor, as shown in Figure, we have

1407_Balanced Wye-Connected Load.png

Note that ¯VBC has been chosen arbitrarily as the reference phasor, as in Figure (b). Assuming the direction of the neutral current toward the load as positive, we obtain

1532_Balanced Wye-Connected Load1.png

That is to say that the system neutral and the star point of the wye-connected load are at the same potential, even if they are not connected together electrically. It makes no difference whether they are interconnected or not.

Thus, for a balanced wye-connected load, the neutral current is always zero. The line currents and phase currents are equal inmagnitude, and the line currents are in phasewith the corresponding phase currents. The line-to-line voltages, in magnitude, are √3 times the phase voltages, and the phase voltages lag the corresponding line voltages by 30°.

The phasor diagram is drawn in Figure(b), from which it can be observed that the balanced line (or phase) currents lag the corresponding line-to-neutral voltages by the impedance

55_Balanced Wye-Connected Load2.png

angle (20° in our example). The load power factor is given by cos 20° for our problem, and it is said to be lagging in this case, as the impedance angle is positive and the phase current lags the corresponding phase voltage by that angle.

The problem can also be solved in a simpler way by making use of a single-line equivalent circuit, as shown in Figure(c),

303_Balanced Wye-Connected Load3.png

in which ¯ VL-N is chosen as the reference for convenience. The magnitude of the line current and the power factor angle are known; the negative sign associated with the angle indicates that the power factor is lagging. By knowing that the line (or phase) currents ¯IA, ¯IB, ¯IC lag their respective voltages ¯VAN, ¯VBN, and ¯VCN by 20°, the phase angles of various voltages and currents, if desired, can be obtained with respect to any chosen reference, such as ¯VBC.


Related Discussions:- Explain balanced wye-connected load

Find the thevenin equivalent of the circuit, (a) Find the Thevenin equivale...

(a) Find the Thevenin equivalent of the circuit shown in Figure (a) at the terminals A-B. (b) Determine the impedance that must be connected to the terminals A-B so that it is m

Counter-controlled analog to digital converter, Q. Counter-controlled analo...

Q. Counter-controlled analog to digital converter? Figure shows the block diagram of a counter-controlledA/Dconverter. Resetting the binary counter to zero produces D/A output

Actual loading method, Actual Loading Method This method is employed c...

Actual Loading Method This method is employed commonly for testing of single phase meters within laboratory. On a meter testing bench that is equipped along with several taps

.branch current method, if a resistor is present between 2 branches in such...

if a resistor is present between 2 branches in such way that its polarities are different to compare with one another so how we choose polarity of that resistor

Determine the required voltage at the high-voltage terminals, Q. A 20-kVA, ...

Q. A 20-kVA, 2200:220-V, 60-Hz, single-phase transformer has these parameters: Resistance of the 2200-V winding R1 = 2.50  Resistance of the 220-V winding R2 = 0.03  Lea

Ldax load accumulator indirect instruction , LDAX  Load Accumulator Indire...

LDAX  Load Accumulator Indirect Instruction This instruction is used to copy data  from memory  location pointed by register  pair only  BC or DE  to the accumulator  HL pair

Working principle of a q meter, Q. Explain the working principle of a Q met...

Q. Explain the working principle of a Q meter. Also explain the factors that cause errors during a Q factor measurement. Ans.   Working Principle of Q Meter: the q meter is

Find the line current after the addition of capacitor bank, Q. Find the lin...

Q. Find the line current after the addition of capacitor bank? A 60-Hz, three-phase motor draws 25 kVA at 0.707 lagging power factor from a 220-V source. It is desired to impro

For the circuit obtain z- and y-parameters, Q. For the circuit shown in Fig...

Q. For the circuit shown in Figure, obtain: (a) z-and y-parameters; (b) Transfer function I 2 /I 1 when V 2 = 0.

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd