Calculate the percent change in load on the wall form tie, Civil Engineering

Assignment Help:

A concrete wall form tie with an ultimate strength capacity of 2,400-lbs is designed for use in a concrete wall form with an 18-in center to center spacing. During formwork inspection it was discovered that the actual spacing is 24-in center to center. Using the actual spacing, the percent change in load on the wall form tie is most nearly: 

765_Calculate the Percent Change in Load on the Wall form Tie.png

Solution:

Determine design tributary area: 1.5-ft x 1.5-ft = 2.25-ft2

Determine actual tributary area: 2-ft x 2-ft = 4-ft2

Determine design ft2 load:    2400-lbs / 2.25-ft2 = 1066.67-lbs/ft2

Determine actual load on 4-ft2:  1066.67- lbs/ft2 x 4-ft2 = 4266.68-lbs

Increase in load is:  4266.68-lbs - 2400-lbs = 1866.68-lbs

Calculate % change = 1 - (4266.68-lbs / 2400-lbs) = 78%

The load increase is 78% on the wall form tie.

 


Related Discussions:- Calculate the percent change in load on the wall form tie

Stiff or soft fenders be designed for berthing in piers, Question Is it...

Question Is it necessary that stiff or soft fenders be designed for berthing in piers? Answer Elasticity of fenders is related to ability to release stored energy duri

Can u give me a sample assignment, im newer to the courses so i would like ...

im newer to the courses so i would like to know about the assignment types. in this case can u please show me a sample assignment?

Purpose of the gap in the road on this bridge, What is the purpose of the g...

What is the purpose of the gap in the road on this bridge? Ans) Purpose of the gap in the road is to permit the road to expand and contract with temperature alters without causi

Concrete, What is Under vibration of fresh concrete?

What is Under vibration of fresh concrete?

Surveying, define surveying and where it is involved

define surveying and where it is involved

Energy dissipation at outlets - typical drainage outlet, Q. Energy dissipat...

Q. Energy dissipation at outlets - typical drainage outlet? Flow velocity at outlets is generally high. Without proper control of this energy, subsequent bank erosion can resu

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd