Meter field testing and installation practices, Electrical Engineering

Meter Field Testing and Installation Practices

Here, we discuss the installation, commissioning and field testing of meters.

Energy Meters - Installation and Commissioning

The meters are linked before the consumer's isolating device (Main Switch) that might be a moulded case miniature circuit breaker, circuit breaker, or an ironclad switch fuse unit. At the time of commissioning, every meter is tested at site through the owner. A reference standard meter of 0.2 classes or better is used for testing.

Supply Side Wiring

The supply side wiring is the responsibility of the utility and the subsequent must be ensured although carrying it out:

a) The supply wires given are of suitable rating.

b) In case of more than one meter on one service line, it is preferable to use bus-bars. While a number of meters are linked to single distributing mains for registering electricity supplied to various consumer loads, separate service lines - phase(s) and neutral, are used for every meter. Each independently metered consumer load is directly linked to distributing mains by its meter connected in specified phase sequence so as to meet accuracy requirements of relevant standard.

c) The supply wire is properly terminated.

d) The connection is as per links diagram mentioned on meter.

e) Utility should use its own earthing for its devices.

Utility gives phase and neutral supply to the consumers. The neutral is used for carrying return current only. The neutral of one consumer should not be linked to other consumers who have independent and separate supply connection. Utility provides separate neutral to every consumer up the metering point and similar is used through the consumer. The consumer ensures in which all the correct wiring practices are followed and neutral is not looped along with another consumer or meters in the similar premises.  Consumer should not earth the neutral after the metering point. While there are multiple meter installations, bus bar arrangement is used for neutral, so that looping is prevented.

Posted Date: 2/6/2013 8:08:25 AM | Location : United States

Related Discussions:- Meter field testing and installation practices, Assignment Help, Ask Question on Meter field testing and installation practices, Get Answer, Expert's Help, Meter field testing and installation practices Discussions

Write discussion on Meter field testing and installation practices
Your posts are moderated
Related Questions
how to design 7 segment design using DSCH2 ?

Case 2 ( A>B) Suppose XX = 05H ( stored  in A ) And  YY = 02H ( stored  in B). Then carry  flag will  reset by CMP instruction, since  A> B in this  case JNC  will transfer the

Why dummy coil is used in wave winding porpose of dc generator

Q. A 300-kVA transformer has a core loss of 1.5 kW and a full-load copper loss of 4.5 kW. (a) Calculate its efficiency corresponding to 25, 50, 75, 100, and 125% loads at unity

1. The voltage across a 1 - μF capacitor is given. Which is the sinusoidal expression for the current? a) 30 sin200t b) 70cos (800t - 20°) 2. At what frequency will the re

Explain n-type and p-type semiconductors. n - Type semiconductor: If small amount of pentavalent impurity (group V elements) is added to a pure semiconductor giving a large

distingish between maximum and minimum modes of operations of 8086 with timing diagrames

On line UPS Systems In this Ups  there are two  switches  one is  main static switch  and another  is Ups  static  switch . in normal  operation the Ups  static switch  remains

what are the most 4 types of doping techinques in semiconductors

Q. Write short note on Quantization? Quantization: This is first step in PCM. Total amplitude range of the modulating signal is divided into a number of standard levels calle