Meter field testing and installation practices, Electrical Engineering

Meter Field Testing and Installation Practices

Here, we discuss the installation, commissioning and field testing of meters.

Energy Meters - Installation and Commissioning

The meters are linked before the consumer's isolating device (Main Switch) that might be a moulded case miniature circuit breaker, circuit breaker, or an ironclad switch fuse unit. At the time of commissioning, every meter is tested at site through the owner. A reference standard meter of 0.2 classes or better is used for testing.

Supply Side Wiring

The supply side wiring is the responsibility of the utility and the subsequent must be ensured although carrying it out:

a) The supply wires given are of suitable rating.

b) In case of more than one meter on one service line, it is preferable to use bus-bars. While a number of meters are linked to single distributing mains for registering electricity supplied to various consumer loads, separate service lines - phase(s) and neutral, are used for every meter. Each independently metered consumer load is directly linked to distributing mains by its meter connected in specified phase sequence so as to meet accuracy requirements of relevant standard.

c) The supply wire is properly terminated.

d) The connection is as per links diagram mentioned on meter.

e) Utility should use its own earthing for its devices.

Utility gives phase and neutral supply to the consumers. The neutral is used for carrying return current only. The neutral of one consumer should not be linked to other consumers who have independent and separate supply connection. Utility provides separate neutral to every consumer up the metering point and similar is used through the consumer. The consumer ensures in which all the correct wiring practices are followed and neutral is not looped along with another consumer or meters in the similar premises.  Consumer should not earth the neutral after the metering point. While there are multiple meter installations, bus bar arrangement is used for neutral, so that looping is prevented.

Posted Date: 2/6/2013 8:08:25 AM | Location : United States







Related Discussions:- Meter field testing and installation practices, Assignment Help, Ask Question on Meter field testing and installation practices, Get Answer, Expert's Help, Meter field testing and installation practices Discussions

Write discussion on Meter field testing and installation practices
Your posts are moderated
Related Questions
Q. Explain the working principle of a Q meter. Also explain the factors that cause errors during a Q factor measurement. Ans.   Working Principle of Q Meter: the q meter is

a) Get the best linear relationship in accordance with least square analysis for the following data:- X 0.9 2.3 3.3 4.5 5.7 6.7 Y 1.1 1.6 2.6 3.2 4.0 5.0 b) The table belo

explain compensation and charge neutrality in GaAs

Q. A 10-kVA transformer is known to have an iron loss of 150 W and a full-load copper loss of 250 W. If the transformer has the following load cycle, compute its all-day efficiency

Q. Explain the classification of amplifiers on the biasing conditions? Based on the amount of transistor bias and amplitude of the input signal, amplifiers can be classified as

Explain the effect of temperature on the resistivity of conducting materials. The resistance of most metals rises with rise of temperature whereas that of semiconductors and el


What is the difference between “Insulating,” “Isolating,” and “Shielded Winding” transformers? Can Acme Transformers be reverse connected? . Can Transformers develop Three Phase po


in DC series generator we consider Eg=V+Ia(Ra+Rse).But in DC shunt generator why it is only Eg=V+IaRa and not Eg=V+Ia(Ra*Rsh/Ra+Rsh)