Determine impedance in each branch - delta connection, Electrical Engineering

Determine Impedance in each branch - delta connection:

A delta connected balanced 3-phase load is supplied from a 3-phase 400 V supply. The line current is 30 Amp and the power taken by the load is 10 kW. Determine

1.      impedance in each branch,

2.      the phase current,

3.      power factor, and

4.      Power consumed if the same load is connected in star.

Solution

Delta Connection Load

Line current IL = 30 Amp

Phase current I ph = 30/√ 3 = 17.32 Amp

(a) Phase impedance Z ph = V ph / I ph  =   400 V/17.32 Amp

                                                                          = 23.095 Ω

(b) Phase current Iph = 30 Amp (already calculated)

(c) Total 3-phase power = 10 kW

     But 3-phase power =  √3 VL  I L cos φ

∴          cos φ=   P/ √3 VL  I L       = 10 × 1000 /√3 × 400 × 30

                                                       = 0.4811

(d) The same power shall be consumed if load is delta connected i.e. 10 kW.

Posted Date: 2/5/2013 2:15:41 AM | Location : United States







Related Discussions:- Determine impedance in each branch - delta connection, Assignment Help, Ask Question on Determine impedance in each branch - delta connection, Get Answer, Expert's Help, Determine impedance in each branch - delta connection Discussions

Write discussion on Determine impedance in each branch - delta connection
Your posts are moderated
Related Questions
Design a recycling MOD 19 up counter using JK FFs. In your design, include the logic circuit diagram and the timing diagram output that counts from 000002 = 010 to 100112 = 1910. C

One circuit has resistor 40? connected in series with inductor  15H and dc voltage 220V. Calculate: i)  Time constant ii)  Current at time (i) iii)  Current at time 0.0

Consider the RC circuit of Figure (a) with R = 2 ,C = 5F,and i(t) = I = 10 A (a dc current source). Find the expressions for the capacitor voltage vC(t) and the capacitor current

Define Shifting and Reversing – Linear System? The signal x[n - m] is said to be time-shifted by m samples, where m is an integer. If m is positive, the shift is to the right (

Energy Conservation Building Codes It encompass the norms and standards of energy consumption expressed in terms of per square meter of the area wherein energy is used. The

Name the switching schemes used in a digital exchange

singly excited magnetic systems

Q. Explain from the drain characteristics that a JFET has  infinite resistance? When V GS = 0v when a positive voltage Vds has been applied across the channel and the gate


Q. Explain working of Ammeter? In order to measure the current through a wire or line of a circuit, an ammeter is connected in series with the line. A practical ammeter can usu