Test Schedule - Meter Testing

The test schedule as per the Central Electricity Authority Regulations on Installation and Operation of Meters is given below.

Table: Test Schedule

Meter Type

Schedule

Single Phase LT meters

Once in 5 years after installation

LT three phase meters (CT operated) 20 kVA to 100 kVA

Once in a year to be checked since these are installed for high value consumers

Other LT metering systems

Once in two years after installation

EHT / HT meters

Below 5 MVA - Once in a year
5 to 10 MVA - Once in six months
above 10 MVA - Once in a quarter

The testing schedule for HT consumers should cover the whole Metering System involving CTs, PTs and Pilot Wire. Detailed ratio testing of CT, PT and control Pilot/ wires is to be completed. Testing by mobile vans/mobile cubicles through secondary injections kit and phantom loading might also be carried out through Measurement Unit. All new meters should meet the needs of Accuracy Class spelt out in Table.

                                                   Table: Requirements of Accuracy Class

Type of Consumer

Overall Accuracy Class

EHT Consumers (33 kV)

0.2

HT Consumer (44 to 33 kV)

0.5 or better

LT Consumer (Whole Current meters)

1.0 or better

LT Consumers (CT operated)

1.0 or better

 


Related Discussions:- Test schedule - meter testing

Induction motor, principle and operation of 3phace induction motor

principle and operation of 3phace induction motor

Bcd to excess 3 code converter, What are the industrial applications of the...

What are the industrial applications of the project bcd to excess 3 code converter?

Design an appropriate system, From a source with P in = 2.4 mW, we want to...

From a source with P in = 2.4 mW, we want to get P out = 60 mW at a distance l = 20 km from the source. α for the transmission line is given to be 2.3 dB/km. The available amplif

Explain basic input output system function call, Discuss BIOS function call...

Discuss BIOS function call with one example. BIO stands for Basic Input Output System: This is a set of programs to give most basic low-level services as services keyboard, s

Zero flag - sub subtract instruction , Zero Flag Since results  is n...

Zero Flag Since results  is non  zero in this  example zero  flag is reset.

What layers are covered under end to end layer connectivity, Q. What layers...

Q. What layers are covered under end to end layer connectivity? Layers 4-7 of ISO-OSI reference model communicate with peer entities in end systems. In intermediate systems,th

What is accelerated graphics port, What is AGP? AGP: The latest additio...

What is AGP? AGP: The latest addition for many computer systems is the inclusion of the accelerated graphics port. This AGP operates at the bus clock frequency of the microproc

Perform octal subtraction, Q. Do as directed. a) Hexadecimal addition: ...

Q. Do as directed. a) Hexadecimal addition: 101 + ABC b) (43.25) 10-(89.75) 10 using 1's Complement c) Octal Subtraction 123-777 d) (123)6 + (435)6 = ( ? )6 e) ABC

Find the voltage regulation and efficiency of the line, Q. A60-Hz, three-ph...

Q. A60-Hz, three-phase transmission line has a total per-phase series impedance of 35+j140 .Ifit delivers 40 MW at 220 kV and 0.9 power factor lagging, find: (a) The voltage, c

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd