The test schedule as per the Central Electricity Authority Regulations on Installation and Operation of Meters is given below.
Table: Test Schedule
Meter Type
Schedule
Single Phase LT meters
Once in 5 years after installation
LT three phase meters (CT operated) 20 kVA to 100 kVA
Once in a year to be checked since these are installed for high value consumers
Other LT metering systems
Once in two years after installation
EHT / HT meters
The testing schedule for HT consumers should cover the whole Metering System involving CTs, PTs and Pilot Wire. Detailed ratio testing of CT, PT and control Pilot/ wires is to be completed. Testing by mobile vans/mobile cubicles through secondary injections kit and phantom loading might also be carried out through Measurement Unit. All new meters should meet the needs of Accuracy Class spelt out in Table.
Table: Requirements of Accuracy Class
Type of Consumer
Overall Accuracy Class
EHT Consumers (33 kV)
0.2
HT Consumer (44 to 33 kV)
0.5 or better
LT Consumer (Whole Current meters)
1.0 or better
LT Consumers (CT operated)
full sub tractor using demultiplexer
Q. For the circuit given in Figure, develop and execute a PSpice program to solve for the node voltages.
Q. Explain the applications of emitter follower. Because of high input impedance and low output impedance an emitter follower is capable of transferring maximum power from the
Q. Explain basic working of Transport Layer? It is responsible for establishing a network independent communication path appropriate for the specific terminal equipments (for exa
Switched Mode Power Supply (SMPS) Switching mode power supply converts an unregulated DC voltage to a regulated DC output voltage . SMPS stands for switched mode power
A bandpass filter design can be accomplished through the cascade connection shown in Figure, where the frequencies between the two cutoffs fall in the passband of both filters and
short note on priming
Define Sampling below the Nyquist Rate? A further reduction of the sampling frequency will reason one sample to be taken each period. The Case 3 plot depicts the effect of this
Types of Meter Test A meter should pass the subsequent two types of tests: Type Tests Routine Tests Meters are calibrated such in which the whole
Q. Frequency stability of quartz crystals ? The amount of frequency deviation from the ambient temperature frequency over the operating temperature range. This deviation is ass
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd