Technical loss in electrical systems, Electrical Engineering

Assignment Help:

Technical Loss in Electrical Systems

Technical loss is inherent in electrical systems, as all electrical devices have a few resistances and the flow of currents causes a power loss (I2R loss). Integration of this power loss over time, i.e. ∫ I2R.dt is the energy loss. Every element in a power system (a line or a transformer) offers resistance to power flow and, therefore, consumes some energy although performing the duty expected of it. The cumulative energy consumed by all these elements is classified as "Technical Loss." Technical losses are because of energy dissipated in the conductors and equipment used for Transmission, Transformation, Sub- transmission and Distribution of Power. These occur at several places in a distribution system - in lines, mid-span joints and terminations transformers, service cables and connections and etc.

Table: Losses Due to Technical Reasons

•  Line losses

•  Loss in conductors/cables where lowersize conductors are used. This causessags and temperature rise in conductorswhich further aggravate the loss,

•  Loss in higher loaded phase wires due to unbalanced loading,

•  Loss due to current in neutral for cases or unbalance where neutral wires of lowersize are used (like 3 ½ core cables, andneutral wires of size lower than phasewires),

•  Loosening of strands (in multi-strandconductors like ACSR, AAC, AAA, etc.). 

•  Loss in mid-span joints

(or any joint) and at

terminations

•  Contacts of joints due to improper installation and looseness,

•  Contacts of joints due to inadequatesurface area of contact.

•  Loss in transformers

(typically DTs)

 

•  Loose connections at bushings,

•  Bend in jumpers at connectors where the strands are not tightly held,

•  High no-load loss depending on type of core used, 

•  High no-load loss in repaired transformers where the core has not been properly tightened,

•  No load loss in case a large number of lightly loaded DTs,

•  High copper loss for transformers operating at sub-optimal loading which is not commensurate with the designed optimal loading. 

•  Loss in service cables

and connections

•  Undersized service cables,

•  Loss in joints of service cables at the poles/junction boxes,

•  Use of inappropriate fasteners without spring washers at the crimped joints.

•  Loss due to high

impedance faults

•  Tree touching, creepers, bird nesting,

•  Insulator breakages and tracking on surface of the insulator.

•  Loss in re-wired

fuses/jumpers

•  Loose connections,

•  Inadequate size of fuse wires - often a source of hot spots.

The magnitude of energy dissipation depends hugely on the pattern of loading of transmission and distribution lines, kinds of loads, design of lines and etc. It is not probable to eliminate such losses inherent in a system altogether. They could, thus, be reduced to some extent. The technical losses could be further sub-grouped depending upon the stage of power transformation and transmission system as Sub-transmission losses (33 kV/11kV), Transmission losses (400 kV/220 kV/132 kV/66 kV), and Distribution losses (11 kV/0.4 kV).


Related Discussions:- Technical loss in electrical systems

Kpi for second stage implementation, KPI for Second Stage Implementation ...

KPI for Second Stage Implementation These KPIs deal along with the quality of the relationship among a supplier and a user (customer). They are significant to potential custom

TTL NAND gate, Q. Explain working of TTL NAND gate? The TTL logic famil...

Q. Explain working of TTL NAND gate? The TTL logic family uses only transistors instead of a combination of transistors and diodes. TTL has the same high and low ranges as DTL.

The operation of colpitts oscillator, Q. Explain with the help of a circuit...

Q. Explain with the help of a circuit diagram,the operation of COLPITTS OSCILLATOR. Oscillator is a circuit used to generate a.c voltage without a.c.input signal.The energy to

Explain power-system loads, Q. Explain Power-System Loads? Figure repre...

Q. Explain Power-System Loads? Figure represents a one-line (single-line) diagram of a part of a typical three-phase power system. Notice the symbols that are used for generato

What is meant by regulation, Q. What is meant by regulation? The output...

Q. What is meant by regulation? The output of most power supplies should be a constant voltage. Unfortunately, this is difficult to achieve. There are two factors that can caus

Dc electric motors, T h er e are three main types -   The Shu...

T h er e are three main types -   The Shunt Connected DC motor in which the armature coils are connected in parallel with the field coils   The Serie

Calculate the voltage regulation, The per-phase synchronous reactance of a ...

The per-phase synchronous reactance of a three-phase, wye-connected, 2.5-MVA, 6.6-kV, 60-Hz turboalternator is 10. Neglect the armature resistance and saturation. Calculate the vo

1- phase full bridge inverter with r- load , 1- phase  Full Bridge Invert...

1- phase  Full Bridge Inverter with R- Load 1-phase full  bridge inverter with resistive load R i it has  advantage over 1-? half  bridge  inverter that it does  not require

Types of multiplexing techniques, (a) List three types of Multiplexing tech...

(a) List three types of Multiplexing techniques. (b) Give two advantages of "Multiplexing". (c) Given the total duration for the signal is 8 ns. What is the bit rate for

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd