Line Protection., Electrical Engineering

Assignment Help:
The Lennox to Bowmanville 500 kV circuit, spanning a distance of about 180 km,
has series (inductive) impedance j 0.0224 pu and shunt (capacitive) admittance j 2.34 pu,
quoted on base values of 500 kV and 100 MVA. Determine the following:
(a) Line charging current (in Amps) drawn by the line when supplied from one terminal
with the supply bus operating at 500 kV (note that system/bus operating voltage is
always quoted on a phase-to-phase basis, unless specified otherwise)
(b) Steady-state phase to ground voltage (in pu) at the opposite line terminal (due to
Ferranti rise) when the line is placed on potential as above. (HINT: For this
calculation, the line is modeled by its nominal-pi representation, with half of the line’s
shunt capacitance connected to ground on each side of the total (series) line
inductance, as depicted below.

Related Discussions:- Line Protection.

Preventing leakages at insulators, Preventing Leakages at Insulators L...

Preventing Leakages at Insulators Leakages at insulators, cracking of insulators and flashover across insulators frequent cause outages and give output in loss of revenue. Pol

Discuss the approximate effect on the characteristic, Consider a three-phas...

Consider a three-phase induction motor with a normal torque-speed characteristic. Neglecting the effects of stator resistance and leakage reactance, discuss the approximate effect

Combinational-sequential, Design combinational-sequential electronic logic ...

Design combinational-sequential electronic logic gate circuit for a car wash....

Square wave generator ( 10 MHz to 20MHz), I need a simple design of above ...

I need a simple design of above mentioned , this oscillator will be used in a wireless power transmission

8085 and 8086 in microprocessor, What is the difference among 8085 and 8086...

What is the difference among 8085 and 8086 in microprocessor? Ans) 8086 has a special concept known as memory segmentation. It permits parallel processing, whereas 8085 does no

Calculate the power factor of the motor, A 3 phase 400 volt(line to line) w...

A 3 phase 400 volt(line to line) wye connected synchronous motor has Xs= 1 ohm per phase and a negligible armature resistance. The field current is so adjusted that the internal(in

FRACTIONAL PID TUING USING GA FOR LOAD FREQUENCY CONTROL, Iam doing my proj...

Iam doing my project on LFC using tuned FOPID.I have considered a two area model..I need help regarding my project.i need help regarding implementation of GA MATLAB code for a two

Radio communication engineering, how electromagnetic wave transmitted from ...

how electromagnetic wave transmitted from the ground are bent back towards the earth when they enter a layer of ionosphere?

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd