Example for beam flexure design, Civil Engineering

Assignment Help:

Example for Beam Flexure Design

Select the lightest W section for the simply supported beam shown below.  The beam length is 12ft.  The nominal loading is: wd = 4.0 kip/ft (including beam weight) and wl = 8.5 kip/ft.  Use grade 50 steel and assume lateral bracing is provided only at the ends of the section.

1823_Example for beam flexure design.png

Solution:

Load Factors are: 1.2 for dead load and 1.6 for live load as per ASCE 7 specifications (these are also shown in the concrete portion of the provided manual).

Wtotal = 1.2*4.0 kip/ft + 1.6*8.5 kip/ft = 18.4 kip/ft

L = 12 ft

Mu = WL2 / 8 = 18.4 kip/ft * (12 ft) 2 / 8 = 331.2 kip*ft

φMn = 331.2 kip*ft

Enter the chart with the moment needed and the unbraced length as shown below:

φMn =331.2, Lb = 12'

Answer : W18x55


Related Discussions:- Example for beam flexure design

Plumbing technology, This assessment will test Learning Outcomes 3 and 4 as...

This assessment will test Learning Outcomes 3 and 4 as well as the component of Learning Outcome 1 as it refers to waste disposal for the Plumbing Technology. The student is expect

Project, I want to do project using ul design directory

I want to do project using ul design directory

Project costing for Engineering success, Hi I am looking for someone who ca...

Hi I am looking for someone who can help to solve my assignment questions in a subject called project costing and I need him to continue with me until I complete this subject. I a

Remedial measures for problems in turbid water - refraction, Define Remedia...

Define Remedial measures for Problems in Turbid Water - Refraction? There is little that can be done to overcome the effects of refraction. Image definition and contrast in tur

Trigo, a pilot entering a bay on course

a pilot entering a bay on course

Explain basic need of design of shock transmission unit, Explain the Basic ...

Explain the Basic requirement of Design of shock transmission unit? The STU must withstand the specified design load. The stroke of the piston must be bigger than the movement

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd