Compute the worst voltage regulation, Electrical Engineering

Assignment Help:

Q. The following data were obtained on a 25- kVA, 2400:240-V, 60-Hz, single-phase distribution transformer:

• Open-circuit test with meters on LV side: 240 V, 3.2 A, 165 W

• Short-circuit test with meters on HV side: 55 V, 10.4 A, 375 W

Compute the worst voltage regulation and the power factor at which it occurs, when the transformer is delivering rated output at rated secondary terminal voltage of 240 V. Sketch the corresponding phasor diagram.


Related Discussions:- Compute the worst voltage regulation

Microprocessor, highest priority interrupt in 8085 microprocessor

highest priority interrupt in 8085 microprocessor

Determine the resistivity of the wire, The resistance of 1.5 km of wire of ...

The resistance of 1.5 km of wire of cross-sectional area 0.17 mm 2 is 150Ω. Determine the resistivity of the wire.

Energy, Explain different stage in energy audit?

Explain different stage in energy audit?

What do you mean by waveforms, Q. What do you mean by Waveforms? We are...

Q. What do you mean by Waveforms? We are often interested in waveforms, which may not be constant in time of particular interest is a periodic waveform, which is a time-varying

Wcdma, what is that mean and explain

what is that mean and explain

Explain about subscriber loop system, Q. Explain about Subscriber Loop Syst...

Q. Explain about Subscriber Loop System? Subscriber Loop System:Each subscriber in a telephone network is connected normally to the nearest switching office by a dedicated pair

Design the synchronous sequential circuit for state diagram, Design the Syn...

Design the Synchronous Sequential Circuit for State Diagram Illustration: - We wish to design the synchronous sequential circuit whose state diagram The kind of flip-f

Explain effect of impurity on conductivity of semiconductor, Explain the ef...

Explain the effect of impurity on the conductivity of a semiconductor. To form a semi-conductor conductive, a small amount of appropriate impurity is added. This is then termed

Multiple tariff meters or tou meters, Multiple Tariff Meters or TOU Meters ...

Multiple Tariff Meters or TOU Meters Time of use metering facilitates load control and planning on the part of utilities. This is efficiently achieved using a concept known as

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd