Compute the worst voltage regulation, Electrical Engineering

Assignment Help:

Q. The following data were obtained on a 25- kVA, 2400:240-V, 60-Hz, single-phase distribution transformer:

• Open-circuit test with meters on LV side: 240 V, 3.2 A, 165 W

• Short-circuit test with meters on HV side: 55 V, 10.4 A, 375 W

Compute the worst voltage regulation and the power factor at which it occurs, when the transformer is delivering rated output at rated secondary terminal voltage of 240 V. Sketch the corresponding phasor diagram.


Related Discussions:- Compute the worst voltage regulation

Discuss the assembler directive of offset, Discuss the assembler directive ...

Discuss the assembler directive of OFFSET with example. OFFSET: This is an operator to find out the offset (displacement) of a variable or process regarding the base

Find the resonant angular frequency, Consider the circuit shown in Figure w...

Consider the circuit shown in Figure with R 0 , (b) the quality factor Q, and (c) the maximum impedance Z m . Comment on the applicability of the universal resonance curve.

Evaluate the current using the loop-current method, Consider the circuit in...

Consider the circuit in Figure (a), which include a controlled source, and find the current in the 5-V source and the voltage across the 5- resistor by using (a) the loop-current

Calculate the cost per bit for dram, A silicon foundry produced 1.2 million...

A silicon foundry produced 1.2 million 8-inch wafers in 1997; how many 600 mil die is that?  The foundry is scheduled to produce 20,000 12-inch wafers per month by the year 2001 us

Evaluate the current flowing in the direction from b to a, Q A beam contain...

Q A beam containing two types of charged particles is moving from A to B. Particles of type I with charge +3q, and those of type II with charge -2q (where -q is the charge of an el

.energy, units of potential energy

units of potential energy

Calculate maximum reactive power the generator can produce, A 3-phase, wye-...

A 3-phase, wye-connected, 11.8 kV, 100 MVA turbo- generator of 0.8 power factor lagging has a synchronous reactance of 2.0 p.u. on rating. The generator is driven by a steam turbin

Successive approximation adc, Successive approximation ADC One method ...

Successive approximation ADC One method of addressing digital ramp ADC's shortcomings is so-called successive approximation ADC. Only change in this design is a very special c

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd