Compute efficiency of 4 hours full load at 0.8 power factor, Electrical Engineering

Assignment Help:

Q. A 10-kVA transformer is known to have an iron loss of 150 W and a full-load copper loss of 250 W. If the transformer has the following load cycle, compute its all-day efficiency:

4 hours full load at 0.8 power factor

8 hours 75% full load at 1.0 power factor

12 hours 50% full load at 0.6 power factor


Related Discussions:- Compute efficiency of 4 hours full load at 0.8 power factor

Logistical management - gis applications, Logistical management - Gis appli...

Logistical management - Gis applications: Using GIS also allows a radical improvement in daily work management practices - such as planning new installations, scheduling opera

Give the register organization of 8257, Give the register organization of 8...

Give the register organization of 8257? The 8257 do the DMA operation over four independent DMA channels. Each of the four channels of 8257 has a couple of two 16-bit registers

Combinational-sequential, Design combinational-sequential electronic logic ...

Design combinational-sequential electronic logic gate circuit for a car wash....

Show that the output will be high, Considering the TTL NAND gate circuit of...

Considering the TTL NAND gate circuit of Figure, with one or more inputs low, show that the output will be high.

Electric Circuit, The manufacturer of a 6V dry-cell flashlight battery says...

The manufacturer of a 6V dry-cell flashlight battery says that the battery will deliver 15 mA for 60 continuous hours. During that time the voltage will drop from 6V to 4V. Assume

Power spectral density, Power Spectral Density: To introduce the P...

Power Spectral Density: To introduce the Power Spectral Density (PSD) of a random signal. To study classical methods for PSD estimation. To investigate model-based

Common-base configuration, Common-base configuration:  The common-bas...

Common-base configuration:  The common-base that is abbreviated as CB transistor configuration, which is as well termed as the 'grounded base' configuration, is displayed in

Transfer function, derive transfer function of S= 2.25+j4.5

derive transfer function of S= 2.25+j4.5

ET1410, MODULE 2 EXERCISE: OP-AMP CONFIGURATION

MODULE 2 EXERCISE: OP-AMP CONFIGURATION

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd