Q. Steam and Power Generation Equipment?
Locating steam and power generation equipment outside of the process areas ensures that critical facilities feeding major portions of the plant are protected from possible fires or explosions in the process areas. Non-critical steam generators (supplying less than 25% of total demand, or only supply a single plant) may be located within a process area with spacing as for fired heaters.
Central services, such as cooling towers, boilers, power stations and electrical substations shall be located centrally but away from hazardous areas so they will neither be affected by a fire or explosion within the plant nor provide a source of ignition for any potential flammable liquid or gas release. Maintain adequate separation between different utility services because utility losses could then lead to unsafe conditions in other plant units, possibly creating fires or explosions. Increase the reliability of utilities by keeping adequate spacing between boilers or generators. Refer to the Appendices for suggested adequate separation between different utilities.
Properly pressurize substations in accordance with NFPA 496 or install separate electrical substations and motor control centers. Locate substations away from hazardous areas to increase the reliability of the power supplies should an accident occur. Bury electrical distribution cables to limit their exposure to explosions, fires, storms and vehicles and to ease fire fighting accessibility.
Determine elongation of bar: A conical bar tapers uniformly from diameter of 4 cm to 1.5 cm in length of 40 cm. If axial force of 80 kN is applied at each end, determine elon
Q. Safety from Corrosive Chemicals? Safety showers and eyewash stations shall be provided in areas where corrosive chemicals are stored and handled. They should be located so t
CAD-CAM Data Exchange: The interface SET transferred information on wire-frames, surfaces, B-representation and FEM models as well as technical drawings and scientific data. I
for a 210 MW unit how we calculate power output at each stage if the turbine has 25 reaction stages
(a) What are the need of a surface condensing ? Write disadvantages and advantages of Jet condenser and surface condenser. (b) A surface condenser is designed to handle 10000 Kg
Q. Explain about Hardness testing? When indicated on equipment or vessel data sheets, hardness testing shall be performed as follows: a) Perform hardness tests at or near th
What are types of raft foundation? Define according to rigid mat deign. One of the common types of raft foundation is the flat concrete slab 0.75 to 2.00 m thick with a two way
Pier and Well Foundations Pier foundations are used when the loads to be transmitted are heavier than loads those can bc acconlplished by piles. They are essentially bearing i
Dead Centre The position of the working piston and the moving parts which are mechanically connected to it, at the moment when the direction of the piston motion is reserved
‘coefficient of insensitiveness’ of governors
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd