Q. Explain the three-line cable Residential wiring?

The three-line cable coming out of the secondaries of the distribution transformer on the utility pole passes through the electric meter that measures energy consumption in kilowatt-hours and terminates at the main panel. Figure 4.4.2 shows a typical wiring arrangement for a residence. At the main panel, circuit breakers serve the joint role of disconnecting switches and overcurrent protection; the neutral is connected to a busbar (bus) and in turn to the local earth ground; the hot lines are connected to individual circuits for lighting and appliances, as illustrated in Figure.

The circuit breaker labeled GFCI (ground-fault circuit interruption), used for safety primarily with outdoor circuits and in bathrooms, has additional features that will be described later. Note that every outgoing "hot" wire must be connected to a circuit breaker, whereas every neutral wire and ground wire must be tied directly to earth ground at the neutral busbar.

Today most homes have three-wire connections to their outlets, one of which is shown in Figure. The need for both ground and neutral connections needs to be explained, since the ground conductormay appear to be redundant, playing no role in the actual operation of a load that might be connected to the receptacle. From the viewpoint of safety, the ground connection is used to connect the metallic chassis of the appliance to earth ground. Without the ground conductor connected to the metal case of the appliance, as shown in Figure(a), the appliance chassis could be at any potentialwith respect to ground, possibly even at the "hot"wire's potential if a part of the "hot" wire were to lose some insulation and come in contact with the inside of the chassis.

An unintended connectionmay occur because of the corrosion of insulation or a loosemechanical connection. Poorly grounded appliances can thus be a significant hazard by providing a path to ground through the body of a person touching the chassis with a hand. An undersized ground loop current limited by the body resistance may flow directly through the body to ground and could be quite harmful. Typically, the circuit breaker would not operate under such circumstances.

422_Explain the three-line cable Residential wiring.png


Related Discussions:- Explain the three-line cable residential wiring

What is polymerised resultant of phenol and formaldehyde, Phenol and Formal...

Phenol and Formaldehyde are polymerised to a resultant product known as (A) PVC.                                  (B) bakelite. (C)  Polyester.                        (D)

Matlab, what is the future scope of matlab in india?

what is the future scope of matlab in india?

Find a minimum two level, Find a minimum two level, multiple-output AND-OR ...

Find a minimum two level, multiple-output AND-OR gate circuit to realize these functions (eight gates minimum). F 1 (a,b,c,d) =Σm(10,11,12,15) +D (4,8,14) F 2 (a,b,c,d) =Σm(4

Electric Circuit, The manufacturer of a 6V dry-cell flashlight battery says...

The manufacturer of a 6V dry-cell flashlight battery says that the battery will deliver 15 mA for 60 continuous hours. During that time the voltage will drop from 6V to 4V. Assume

Give the alternate functions for the port pins of port3, Give the alternate...

Give the alternate functions for the port pins of port3? RD - Read data control output. WR - Write data control output. T1 - Timer / Counter1 external input or test pin.

Show balanced three-phase loads, Q. Show Balanced three-phase loads? Th...

Q. Show Balanced three-phase loads? Three-phase loads can be connected in either wye (also known as star or Y) or delta (otherwise known as mesh or ). If the load impedances i

Energy band diagram, E n e r gy Band Diagram Energy band d...

E n e r gy Band Diagram Energy band diagram in qualitative form is sketched by following the following process: 1. The semiconductor device is supposed to be ma

Common control switching system, Q. Common control switching system? C...

Q. Common control switching system? Common Control Switching System: A functional block diagram of a common control switching system is displayed in Figure. Control functions

Compute the source current, Q. A 230-V, single-phase, 60-Hz source supplies...

Q. A 230-V, single-phase, 60-Hz source supplies two loads in parallel. One draws 10 kVA at a lagging power factor of 0.80 and the other draws 6 kWat a lagging power factor of 0.90.

Bad workmanship, Bad Workmanship Bad workmanship contributes important...

Bad Workmanship Bad workmanship contributes importantly towards increasing distribution losses. Efforts should, thus, be made to have the best probable workmanship. In this co

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd