Evaluate Phase difference between voltage and current:
An inductive coil of reactance 15.7 Ω and resistance 32 Ω is connected in series with a capacitor of reactance 79.5 Ω. The circuit is connected across 500 V AC supply, Find out
1. Current,
2. Phase difference between voltage and current,
3. Magnitude of voltage across the inductive coil, and
4. Total power absorbed.
Solution
Figure for Example
R = 32 Ω, X = XL - XC
= - 63.8 Ω (circuit in capacitive)
Impedance Z = R - jX = 32 - 63.8 j Ω
(a) Current i = v / Z = 500 ∠ 0o / 32 - 63.8 j
= 7 ∠ 63.36o Amp
(b) Angle between V and i
φ = 63.36 (leading)
(c) Impedance of coil, ZL = R + j XL = 32 + j 15.7
| Z L | = 35.6439 Ω
Voltage across coil = I ZL = 7 × 35.6439
= 249.5075 Volt
(d) Power absorbed = I2 R = 72 × 32 = 1568 watts
MATLAB
its defination and mathematical expression if any
barrier voltage at pn junction
Metering and Billing System Previously, you have learnt about various measures for reducing commercial losses of a utility. You have studied in which the metering and billing
The system diagram for the proposed unit is shown below. The system operates on the principle of Time to Rate Conversion. Signals from the heart beat sensor are amplified
Technical Loss Reduction - Power Supply 1. Technical loss reduction could be achieved through several measures such as network reconfiguration, load balancing, network recondu
For the 3-bit 2 n -R D/A converter of Figure, calculate the analog output voltage when the input is (a) 100, and (b) 010. Solution a. For the binary input 100, switches con
Module of the rated currents - transformer: The transformer of the Face(Figure) 2 is a transformer of type Delta-Y (the neutral of Y is grounded). The rated output is of 1500
The LEDs should also show the rounded percentage of the full scale output. Since there are 8 LEDs every one represents 12.5%. Though, since we want the rounded percentage the LED o
A three-phase, wye-connected, cylindrical-rotor synchronous generator rated at 10 kVA and 230 V has a synchronous reactance of 1.5per phase and an armature resistance of 0.5 pe
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd