Determine the efficiency when the transformer, Electrical Engineering

Assignment Help:

A 3-kVA, 220:110-V, 60-Hz, single-phase transformer yields these test data:

• Open-circuit test: 200 V, 1.4 A, 50 W

• Short-circuit test: 4.5 V, 13.64 A, 30 W

Determine the efficiency when the transformer delivers a load of 2 kVA at 0.85 power factor lagging.


Related Discussions:- Determine the efficiency when the transformer

Find the number of possible station frequencies, Q. Find the number of poss...

Q. Find the number of possible station frequencies in the AM broadcast system in the United States

Explain relative data addressing mode, Explain relative data addressing mod...

Explain relative data addressing mode (with examples) available in microprocessors. Relative Mode: Operand supplied is an offset, not the actual address. Added the con

Calculate the frequencies at which there is an alias, A pure sine wave alon...

A pure sine wave along with a frequency of 100Hz is sampled at 150Hz. At which point one of the subsequent frequencies would you expect an alias? A) 75Hz B) 100Hz C) 150Hz

Automatic meter reading and remote meter reading, Automatic Meter Reading a...

Automatic Meter Reading and Remote Meter Reading Automatic Meter Reading (AMR) and Remote Meter Reading (RMR) elaborate several systems which permit meters to be checked with

Lhld load hl pair direct instruction, LHLD  Load  HL Pair Direct  Instru...

LHLD  Load  HL Pair Direct  Instruction This  instruction is used to copy the  content  of memory  location specified  by opened  in register L  and copy the content of next  m

Derive an expression for the electric force, Q. A two-winding system has it...

Q. A two-winding system has its inductances given by where k 1 and k 2 are constants. Neglecting the winding resistances, derive an expression for the electric force when

Find the resistor values of rc, Apply the rule-of-thumb dc design presented...

Apply the rule-of-thumb dc design presented in this section for a silicon npn BJT with β = 70 when the operating Q point is defined by I CQ = 15 mA and I BQ = 0.3 mA, with a dc s

Determine the voltage at the load terminals, Two single-phase 60-Hz sinusoi...

Two single-phase 60-Hz sinusoidal-source generators (with negligible internal impedances) are supplying to a common load of 10 kW at 0.8 power factor lagging. The impedance of the

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd