A 3-phase, 16-pole synchronous machine is driven by a prime mover at a speed of 600-rpm with the stator open circuited. The rotor flux per pole is 0.025-Wb. Determine
(a) the frequency and rms value of the induced voltage in the stator per phase having 450 effective turns;
(b) line voltage for the Y-connected machine.
Solution:
(a) The frequency of the stator voltage is from (1.1): f = pn/60 = 8.600/60 = 80-Hz.
The voltage generated per phase is using (1.4):
Eφ = 4.44 .80.450.0.025 = 3996 - V ≈ 4 - kV.
(b) The voltage across the stator terminals (line-to-line) is VLL = √3. 3996 = 6921.3 -V.
Q. (a) In the circuit shown in Figure the zener diode (with zero zener resistance) operates in its reverse breakdown region while the voltage across it is held constant at VZ and t
The basic operation of battery A simple cell comprises two dissimilar conductors (electrodes) in an electrolyte. Such a cell comprises copper and zinc electrodes. An electric
Q. Two three-phase generators are supplying to a common balanced three-phase load of 30 kW at 0.8 power factor lagging. The per-phase impedance of the lines connecting the generato
OBJECTIVES OF NEP: Access to Electricity for whole households within the next five years. Availability of Power to be ensured to meet the demand through 2012. Pe
what are accidents in an organisation
Error-Rate Control, Output-Rate Control, and Integral-Error (Reset) Control Let us consider a typical second-order servomechanism(containing two energy-storing elements) whose
Ask question #Minimum 100A light assembly shop, 15 m long, 9 m wide and 3 m up to trusses is to illuminated to a level of 200 lux. The utilization and maintenance factors are resp
plz give ans about signs of capicitor, and give detail about clampers.
Dry type 10KVA-3ph-440/230v Dyn11. If we decide to wound above such specification, what current to be taken i.e. phase current or line current 7.57A or 13.12A
CALCULATION OF SERIES DC MOTOR
Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!
whatsapp: +91-977-207-8620
Phone: +91-977-207-8620
Email: [email protected]
All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd