Q. Design layout of Storage Tanks in plant?

Generally, tanks taking up large areas of the plot are located off-site and storage tanks containing the same product grouped together, spaced within a diked area to contain any leakage. A dike must be sized to have a volumetric capacity of not less than 110% of the capacity of the tank when the diked area contains one tank or when the diked area contains more than one tank, the dike area volumetric capacity must not be less than:

a) The capacity of the largest tank located in the diked area plus

b) 10% of the greater of

i. The capacity of the largest tank), or

ii. The aggregate capacity of all other tanks located in the diked area.

Sizing of diked areas should be established as a priority early in the site layout. Transfer pumps should be outside the berm. Since piping involved in ground fires usually fails within 10 or 15 min. of initial exposure, locate an absolute minimum amount of piping, valves and flanges within dikes. It is also important to install pumps, valve manifolds and transfer piping outside dikes or impounding areas. For the same reason piping for one tank (or group of tanks) should not pass through a dike enclosure of another tank or group of tanks.


Related Discussions:- Design layout of storage tanks in plant

Motion of two bodies - rough surface and smooth pulley, Motion of two bodie...

Motion of two bodies - rough surface and smooth pulley: THE HORIZONTAL SURFACE IS ROUGH AND THE STRING IS PASSING OVER SMOOTH PULLEY. Figure shows two weights W 1 and W 2

Corrosion assessment for mvc evaporator system, Q. Corrosion Assessment for...

Q. Corrosion Assessment for MVC Evaporator System? Typical evaporator systems in SAGD plants operate under extremely severe corrosive conditions due to high chloride content, e

The same magnitude as it did at the bottom, For the normal force in Figure ...

For the normal force in Figure to have the same magnitude at all points on the vertical track, the stunt driver must adjust the speed to be different at different points. Suppose,

Firing rate demand for steam generator, Q. Firing Rate Demand for Steam Gen...

Q. Firing Rate Demand for Steam Generator? The firing rate for each Steam Generator is proportional to the feedwater flowing into that Steam Generator. Thus, the sum of the pa

Illustrate the babcock and wilcox boiler, How the boiler are classified? Sk...

How the boiler are classified? Sketch and define the babcock & Wilcox boiler and also Compare the water tube boiler and fire tube?

Feedwater controls for steam generator, Q. Feedwater Controls for Steam gen...

Q. Feedwater Controls for Steam generator? associated with that Steam Generator. The flow controllers utilize regular P.I.D. controllers, and their outputs are fed directly to

Fundamental geometric transformation, Fundamental geometric transformation:...

Fundamental geometric transformation: The fundamental geometric transformation is Rotation, Translations and Scaling. Other transformations involve reflection and shearing. Tr

Compare two stroke with four stroke engine, Compare Two Stroke with four st...

Compare Two Stroke with four stroke Engine: T w o Stroke Engine In two stroke engine all the four operation that is suction, compression, ignition and exhaust are compl

Design of the microprocessor control system, 1 Prepare a suitable system Me...

1 Prepare a suitable system Memory Map over the first 3K of memory, a suitable PIO configuration and associated Z80 PIO initialisation words in order to support a single electro-hy

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd