Design a sanitary branch sewer, Civil Engineering

Assignment Help:

Q. For what capacity would you design a sanitary branch sewer to serve a section having a population of 12500 persons with a rate of supply of 135 Liters.

Ans.- Average flow equals - 12500 x 135 = 1692500 Liter / day.

                                              = 1692500 / 24 x 60 x 60 = 19.6 Liter / sec.

Making allowance for variation max 3 time of Qty for intensity of flow -

19.6 x 3 = 58.8 Liter / sec. = 0.06 cum / sec.

But this quantity represents only 2/3rd fill there fore full capacity of sewer

= 1.5 x 0.06 = 0.09 cum / sec      for which the section is designed

Assuming a velocity of 1.00 m / sec.    ,     A = Q / V  = πD2 / 4 V ,    D2 = 4 Q / πV

D = √ 4 Q / πV = √ 4 x 0.09 / 3.14 x 1.00 =  0.34 m.

A sewer of 350 mm dia could be used.


Related Discussions:- Design a sanitary branch sewer

Explain chezy manning equation, Explain Chezy Manning Equation v = 1.49...

Explain Chezy Manning Equation v = 1.49/n (R) 0.67 (S) 0.5     R = hydraulic radius (ft) = Area/ wetted perimeter, R = D/4 for circular channels full and one-half full

Examine the state of stress at the junction of flange, Examine the state of...

Examine the state of stress at the junction of flange: A beam of I-section as shown in Figure (a) is subjected to a bending moment of 84.928 kN m and a shear force of 106.1 kN

Can u give me a sample assignment, im newer to the courses so i would like ...

im newer to the courses so i would like to know about the assignment types. in this case can u please show me a sample assignment?

Survey, explain ranging and reciprocal ranging

explain ranging and reciprocal ranging

Simple bending, In case of simple bending after simply supported beam, deri...

In case of simple bending after simply supported beam, derive that M/I = s /y = E/R.

Corrosion protection of lifting anchors in precast concrete, Q. Corrosion p...

Q. Corrosion protection of lifting anchors in precast concrete? Corrosion of lifting anchors in precast concrete units has to be prevented since the corroded lifting units caus

Dam, Check for stability in a dam

Check for stability in a dam

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd