current trasnsformer, Electrical Engineering

Assignment Help:
A 13.8 kV feed er circui t breaker has a 600:5 multira tio curr ent
transform er with charact eristics as show n in Figure 5.11. Th e max -
imum load on the feed er is 80 A pri mary. Phase time inve rse overcurrent
relays are connec ted to the CT secon daries. The relay burden
is 3.2 VA at the tap values selected, and the lead burden is 0.38 V.
a. If the 100:5 CT ratio is used, then a relay tap of 5 A is required in order
for the relay pickup to be 125% above the maximum load. With these,
determine the minimum primary current to just operate the relays.
b. For the select ion of part a what is the appro ximate maximu m
symme trical fault curr ent for whi ch the CTs will not saturate
(use the ANS I=IEEE knee point)?
c. If the 200:5 CT ratio is used so that the 2.5 A relay tap can be used,
determine the minimum primary current to just operate the relays.
13.8 kV
Bus Load bus
Equivalent
source
MVASC = 312.5
Z0 = 11.93 ?8 pu
On 100 MVA base
On 100 MVA base
X1 = X2 = j 0.42 pu
X0 = j 1.26 pu
X2 = 0.15 pu
X0 = 8
4 MVA load
@ 0.9 pf
@ 4 MVA
FIGURE P4.3
 2006 by Taylor & Francis Group, LLC.
d. Repeat part b for the selection of part c.
e. Which of thes e two CT and relay select ions would you recommend ?

Related Discussions:- current trasnsformer

Constant frequency system, Constant Frequency System In this  system c...

Constant Frequency System In this  system chopping period  T is kept constant but the  on time T om is varied. This  system is also referred to pulse with modulation or time

Define the term paging unit, Define the term Paging Unit. Paging Unit:...

Define the term Paging Unit. Paging Unit: The paging mechanism functions along with 4K - byte memory pages or along with a new extension obtainable to the Pentium with 4M byt

What are cu and neu in 8087, What are CU and NEU in 8087? CU-Control un...

What are CU and NEU in 8087? CU-Control unit NEU- Numeric extension unit. The numeric extension unit implements all the numeric processor instructions whereas the control un

Illustrate core losses in magnetic core material, Q. Illustrate Core Losses...

Q. Illustrate Core Losses in magnetic core material? Iron-core losses are usually divided into two components: hysteresis loss and eddy-current loss. The former is proportional

Explain phase-shift keying, Q. Explain phase-shift keying? In PSK, the ...

Q. Explain phase-shift keying? In PSK, the phase angle of a carrier is keyed between two values. When the values are separated by π radians, it is known as phase-reversal keyin

Substation preventive maintenance scheduling optimization, Introduction: ...

Introduction: The scheduling system that is followed by the maintenance department is not well established and is dependable on employee's personal judgment. There were a lot o

Electricity hazards in the laboratory, ELECTRICITY HAZARDS IN THE LABOR...

ELECTRICITY HAZARDS IN THE LABORATORY : You've probably read about, or heard of, people falling onto high voltage rails or cables and surviving thousands of volts. As a contra

Compute the terminal voltage and current of each generator, Q. Three dc gen...

Q. Three dc generators are operating in parallel with excitations such that their external characteristics are almost straight lines over the working range with the following pairs

Temperature triggering , Temperature Triggering At high temperature th...

Temperature Triggering At high temperature the leakage current  of junction J 2 increases. This leakage  current is collector  current of tr 1 and Tr 2 . So rise in temperat

Transformer onnection, what is difference between scot and delta connection...

what is difference between scot and delta connection.

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd