Checking at site - testing of meter, Electrical Engineering

Assignment Help:

Checking at Site - Testing of Meter

The routine testing of meters should be carried out once in 3 years. Further, surprise checks should be conducted at the consumer's installation and meters should be checked from time to time. The significant points to be paid attention to although checking are given below.

Checklist of Important Points for Checking at Site

i) Connections of meter are proper.

ii) Seals are not tampered with.

iii) No loose or direct connections exist.

iv) Meter is not damaged to record less.

v) CTs are properly linked.  No reversal of any phase connection exists. There are multiplying factor is properly calculated and applied.

vi) Meter is well protected from rain, vermin's and dust etc.

vii) Links are connected.

viii) Terminal block is not damaged.

Along with the help of load current of known magnitude (preferably of resistive type) and a wrist watch having a second's hand, you could off hand check at site the performance of the meter as also its accuracy to a few extent.


Related Discussions:- Checking at site - testing of meter

Determine the circuit of three transistors dynamic ram cell, a. Determine t...

a. Determine the circuit of three transistors dynamic RAM cell and define briefly read and write functions. b. Write short note on factors influencing choice of layer for wiring

Motor., if load is removed so which motor will run fast? series or shunt?

if load is removed so which motor will run fast? series or shunt?

Draw a circuit using the cascade system, Design and draw a circuit using th...

Design and draw a circuit using the cascade system to operate two cylinders (A and B) which, on the operation of a start valve, produces the sequence A - B + B - A+. The cylinder

Erc and kpi, ERC and KPI The company requires understanding the strate...

ERC and KPI The company requires understanding the strategic and nearing term impact of the Regulator's orders / tariff approval process. Once these dimensions are understood,

Three byte instruction , Three byte instruction The  instruction which...

Three byte instruction The  instruction which  have 16  bit data address  as its  operand  are three byte  instruction. They  need three  memory  locations to store  them in m

Decision making, Decision  Making The rhombus diamond symbol  is used...

Decision  Making The rhombus diamond symbol  is used to represent  the decision making  process  as shown  below.                                          Figure  De

#linear programming with all three constraints.., #z =x1+2.5x2, with constr...

#z =x1+2.5x2, with constraints, x1+x2>=2, x2 x1+x2 x1=3.question..

Dc simulation component, Once you are happy with the biasing components you...

Once you are happy with the biasing components you will need to disable the DC simulation component and enable the SP component. (Right click the component and then select the "com

Calculate rotor copper losses, A 20 h.p. , 3 phase, 400 volt, 60 hertz, 4 p...

A 20 h.p. , 3 phase, 400 volt, 60 hertz, 4 pole induction motor delivers full load at 5% slip. The mechanical rotational losses are 400W. Calculate (a) The electromagnetic torqu

How many types of buses are, There are three types of buses. Address bu...

There are three types of buses. Address bus: This is used to carry the Address to the memory to get either Instruction or Data. Data bus : This is used to take the Data from

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd