Q. A single-phase, 10-kVA, 2300:230-V, 60-Hz, two-winding distribution transformer is connected as an auto transformer to step up the voltage from 2300 V to 2530 V.

(a) Draw a schematic diagram of the arrangement showing all the voltages and currents while delivering full load.

(b) Find the permissible kVA rating of the auto transformer if the winding currents are not to exceed those for full-load operation as a two winding transformer. How much of that is transformed by electromagnetic induction?


Related Discussions:- Two-winding distribution transformer

Matlab help, hello i have MATLAB 2013 how can i send and receive files usi...

hello i have MATLAB 2013 how can i send and receive files using Bluetooth

Balanced score card and key performance indicators, Balanced Score Card and...

Balanced Score Card and Key Performance Indicators Every successful organization measures its performance across the subsequent parameters, for dissemination to all stakeholde

What is dtmf dialling, Q. What is DTMF dialling? DTMF dialling 1. ...

Q. What is DTMF dialling? DTMF dialling 1.  Uses push buttons 2.  Uses 8 different frequencies in pairs. 3.  16 different characters can be represented. 4.  The f

Matlap code, matlap code to solve the fast decoupled method

matlap code to solve the fast decoupled method

Microgrid, how to connect some DG together?

how to connect some DG together?

Explain working of voltmeter, Q. Explain working of Voltmeter? In order...

Q. Explain working of Voltmeter? In order tomeasure the potential difference between two terminals or nodes of a circuit, a voltmeter is connected across these two points. A pr

Kirchoff''s current law, Kirchoff's Current Law The total current ent...

Kirchoff's Current Law The total current entering a node in a circuit is equal to the total current leaving that node. A Node is a junction between two or more components.

Determine the apparent power and the reactive power, Q. A balanced electric...

Q. A balanced electrical industrial plant load of 9.8 MW with 0.8 lagging power factor is supplied by a three-phase 60-Hz system having a maximum rating (load-carrying capacity) of

3 phase 4 wire meters, 3 Phase 4 Wire Meters 3-phase 4 wire meters (10...

3 Phase 4 Wire Meters 3-phase 4 wire meters (10/20, 20/50 A) are used for agricultural and industrial consumers. For loads up to 50 A, the meters are directly linked to the su

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd