Calculation of receiving end voltage, Electrical Engineering

Assignment Help:

Calculation of Receiving End Voltage

Consider the simple circuit shown in Figure.

333_Calculation of Receiving End Voltage.png

To find the voltage V2 using analytical method:

  P = I V2 = 0.5      ..... (1)

 V2 = V1 - R I      ..... (2)

 V2 = 1 - 0.1 I

∴  0.5 = I ( 1 - 0.1 I ) = I - 0.1 I2 

or I2 - 10 I + 5 = 0        ..... (3)

So I = 10 + √ 100 -20 / 2 = 10 + 8.944272 / 2 = 0.527864 or 9.472 p.u.

∴ V2 = 1 - 0.1 × 0.527864 = 0.9472136 p.u.

Using   I = 9.472 p.u.   gives an unacceptable solution.

Using iterative method, V2 may be found as:

(i) Assume V2 (call it 1V2)

(ii) Find I = P / V2

(iii) Find ?V = R I

(iv) Find new value of V2 = V1 - R I ( call it 2V2)

(v) Check |2 V2 - 1V2|

Solving the previous example by the iterative method gives:

2133_Calculation of Receiving End Voltage 2.png

Notice the improvement in the new value of V2 and the absolute error |2V2 - 1V2|. The calculation may be terminated at the end of any iteration depending on the required accuracy |2V2 - 1V2|.


Related Discussions:- Calculation of receiving end voltage

Accidents, what are accidents in an organisation

what are accidents in an organisation

Reflection and retraction in cables and their calculations, How do I calcul...

How do I calculate the line-cable and cable-line values of reflection and refraction coordinates?

A transistor has how many p-n junction, A transistor has (A) One p-n j...

A transistor has (A) One p-n junction.  (B) Two p-n junction. (C) Four p-n junction. (D) Five p-n junction. Ans: A transistor has two p-n junctions.

Holding current - thyristor , Holding current The holding  current i...

Holding current The holding  current is  the value  of on state  current  required  to maintain  conduction once the  device  the device has  fully timed  on and  the  gate

Compute the generator efficiency at full load, Q. A 100-kW, 230-V, dc shunt...

Q. A 100-kW, 230-V, dc shunt generator, with R a = 0.05 , and R f = 57.5  has no-load rotational loss (friction, windage, and core loss) of 1.8 kW. Compute: (a) The generato

What is the per-unit slip at full load, Q. A three-phase, 60-Hz induction m...

Q. A three-phase, 60-Hz induction motor runs at almost 1800 r/min at no load, and at 1710 r/min at full load. (a) How many poles does the motor have? (b) What is the per-unit

Multi-link connection in a network of register, Q. Multi-link connection in...

Q. Multi-link connection in a network of register? For a multi-link connection in a network of register- controlled exchanges, a register in originating exchange receives addre

Determine phase - voltage and power, Determine phase - voltage and power: ...

Determine phase - voltage and power: A balanced star connected load is supplied from a symmetrical 3-phase 440 Volt system. The current in each of the phase is 40 Amp and lags

Explain role/purpose of dummy coils in dc machine winding., Dummy coils : ...

Dummy coils : These coils are used with wave winding and resorted to when the requirement of the winding are not met by the standard armature punching available in armature win

How can a jfet be used as a constant current source, Q. How can a JFET be u...

Q. How can a JFET be used as a constant current source? Explain from the drain characteristics. As the VDS voltage is increased from 0 to a few volts, the current will increase

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd