Next, let us consider the case of a balanced delta-connected load with impedance of 5 45° supplied by a three-phase, three-wire 100-V system, as shown in Figure (a). We shall determine the line currents and draw the corresponding phasor diagram. With the assumed positive phase sequence (A-B-C) and with ¯VBC as the reference phasor, the line-to-line voltages ¯VAB, ¯VBC, and ¯VCA are shown in Figure. The rms value of the line-to-line voltages is 100 V for our example. Choosing the positive directions of the line and phase currents as in Figure(a), we have

2166_Illustrate Balanced Delta-Connected Load.png

By the application of Kirchhoff's current law at each of the vertices of the delta-connected load, we obtain

858_Illustrate Balanced Delta-Connected Load1.png

2349_Illustrate Balanced Delta-Connected Load2.png

2162_Illustrate Balanced Delta-Connected Load3.png

The phasor diagram showing the line-to-line voltages, phase currents, and line currents is drawn in Figure(b). The load power factor is lagging, and is given by cos 45°. For a balanced delta-connected load, the phase voltages and the line-to-line voltages are equal in magnitude, and the line voltages are in phase with the corresponding phase voltages.

1261_Illustrate Balanced Delta-Connected Load4.png

The line currents, in magnitude, are √3 times the phase currents, and the phase currents lead the corresponding line currents by 30°. The preceding example can also be solved by the one-line equivalent method for which the delta-connected load is replaced by its equivalent wye-connected load. The single-line equivalent circuit is shown in Figure(c). The details are left as an exercise for the student.


Related Discussions:- Illustrate balanced delta-connected load

Controls and system, transfer function of Lube Oil Cooler Temperature

transfer function of Lube Oil Cooler Temperature

Compute the percentage change, Q. A particular BJT has a nominal value of α...

Q. A particular BJT has a nominal value of α 0.99. Calculate the nominal β.If α can easily change ±1%, compute the percentage changes that can occur in β.

Logic circuits, : A farmer owns two barns; one north of a creek and the oth...

: A farmer owns two barns; one north of a creek and the other south of the creek. The farmer has a Cabbage, a Goat, and a Wolf. The Farmer needs to put each item in a barn every ni

Oscilloscope probe compensation, Q.   what is oscilloscope probe compensati...

Q.   what is oscilloscope probe compensation and how is it adjusted?  What effects are noted when the compensation is not correctly adjustment? Direct Probe: This probe  is

#boiler troubles, Ask question #Minimum 300 words accepted#

Ask question #Minimum 300 words accepted#

What do you mean by sub address, Q. What do you mean by sub address? A ...

Q. What do you mean by sub address? A sub address, though a part of the ISDN address, isn't considered as an integral part of the numbering scheme. Sub address is carried in a

Math, How you write this number in letters. 20,000.000.000

How you write this number in letters. 20,000.000.000

Gis application, GIS APPLICATION IN THE POWER DISTRIBUTION ENVIRONMENT ...

GIS APPLICATION IN THE POWER DISTRIBUTION ENVIRONMENT Previously, we have discussed the IT applications in the areas of Metering, Data Acquisition and Management, Asset Manage

Address bus - bus organisation , Address Bus The address  bus is the gr...

Address Bus The address  bus is the group  of 16 lines. It is used  to carry  the address of memory  location and  addresses  of input  and output  ports as shown. It is a unid

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd