For combined load calculate real power and reactive power, Electrical Engineering

Assignment Help:

Q. A 6.6-kV line feeds two loads connected in parallel. Load A draws 100 kW at 0.6 lagging power factor, and load B absorbs 100 kVA at 0.8 lagging power factor.

(a) For the combined load, calculate the real power, reactive power, volt-amperes, and line current drawn from the supply.

(b) If the power factor on the supply end is to be unity, determine the value of the capacitance to be placed across the load if the frequency of excitation is 60 Hz.


Related Discussions:- For combined load calculate real power and reactive power

Power electronics, A step-down transformer has primary turns Np = 100; seco...

A step-down transformer has primary turns Np = 100; secondary turns Ns = 10; primary winding resistanceRp = 100 ?; secondary winding resistance Rs = 2 ?. Assume that there is no l

Find the value of the induced emf, Q. A six-pole, double-layer dc armature ...

Q. A six-pole, double-layer dc armature winding in 28 slots has five turns per coil. If the field flux is 0.025 Wb per pole and the speed of the rotor is 1200 r/min, find the value

What digits are represented by the signal, A signal stands for 0110 with po...

A signal stands for 0110 with positive logic in which low stands for 0 and high stands for 1. If negative logic (in which low stands for 1 and high stands for 0) is used, what digi

Atomic structure, State the postulates of Bohr''s atomic model. Write any ...

State the postulates of Bohr''s atomic model. Write any three merits and demerits.

Calculate the power required from power plant, You will develop a simulatio...

You will develop a simulation that will consist of the following five components: Controller: This script component controls the simulation. It shall permit the user to: 1. C

Minimize f in a pos form and obtain a possible realization, Q. The truth ta...

Q. The truth table for F(A,B,C) = Mi (0, 1, 6, 7) is as follows: (a) Express F in a canonical product-of-sums form. (b) Minimize F in a POS form and obtain a possible re

The a.c/d.c. generator - electromagnetic torque, Note, the armature curren...

Note, the armature current is produced in pulses as the armature rotates under the poles, so the torque also pulsates. This can give rise to extra wear on bearings and the engin

What is interrupt service routine, What is interrupt service routine? I...

What is interrupt service routine? Interrupt means to break the sequence of operation. Whereas the CPU is executing a program an interrupt breaks the normal sequence of impleme

Compute the kvar and the power factor of the motor, Q. A three-phase balanc...

Q. A three-phase balanced load draws 100 kW at 0.8 power factor lagging. In order to improve the supply power factor to 0.95 leading, a synchronous motor drawing 50 kWis connected

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd