Find out form factor and peak factor, Electrical Engineering

Assignment Help:

Find out Form factor and Peak factor:

For the output of full wave rectifier, find out

(a) RMS value,

(b) Average value,

(c) Form factor, and

(d) Peak factor.

Solution

The output current of full wave rectifier

Time period = π

1816_Find out Form factor and Peak factor.png

(c) Form factor K f  = Irms / Iav  =0.707 Im/0.637 Im

(d) Peak factor K =  Im/ Irms  = Im /0.707 Im= 1.414


Related Discussions:- Find out form factor and peak factor

Describe the magnetic effects of current, 1.   Describe the magnetic effe...

1.   Describe the magnetic effects of current? ( to achieve a pass grade, describe the magnetic effect of current) 2.   Complete the diagram to show the direction of mo

Test, current and voltage

current and voltage

Distinguish between ferromagnetic and diamagnetic materials, Distinguish be...

Distinguish between ferromagnetic and diamagnetic materials, mentioning at least one example of each. Ferromagnetic Materials: These are materials wherein magnetic dipoles in

Transistor, can you differentiate the alpha,beta and gamma

can you differentiate the alpha,beta and gamma

What is rxd, What is RXD? RXD- Receive Data Input This input pin of ...

What is RXD? RXD- Receive Data Input This input pin of 8251A gets a composite stream of the data to be received by 8251A.

Draw the power triangle for each load, Q. Two balanced, wye-connected, thre...

Q. Two balanced, wye-connected, three-phase loads are in parallel across a balanced, three - phase 60- Hz, 208-Vsupply. The first load takes 12 kWat 0.6 power factor lagging, and t

Dual-ramp analog to digital converter, Q. Dual-ramp analog to digital conve...

Q. Dual-ramp analog to digital converter? Figure (a) shows the block diagram of a dual-ramp (dual-slope) A/D converter. After a start-of-conversion pulse, the counter is cleare

Explain basic principle of linear sweep voltage generator, Q. Explain the b...

Q. Explain the basic principle of linear sweep voltage generator A linear time base generator or sweep generator is one that provides an output waveform, a portion of which exh

Induced emf, applications of dynamically induced emf

applications of dynamically induced emf

Calculate sending-end voltage at 0.9 pf lagging, A three-phase, 34.5-kV, 60...

A three-phase, 34.5-kV, 60-Hz, 40-km transmission line has a per-phase series impedance of 0.2+j0.5/km. The load at the receiving end absorbs 10 MVA at 33 kV. Calculate the follow

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd