Explain working of three-phase transformers, Electrical Engineering

Assignment Help:

Q. Explain working of three-phase transformers?

Transformation in three-phase systems can be accomplished in either of two ways: (1) connecting three identical single-phase transformers to form a three-phase bank (each one will carry one-third of the total three-phase load under balanced conditions); or (2) a three-phase transformer manufactured for a given rating. A three-phase transformer, compared to a bank of three single-phase transformers, for a given rating will weigh less, cost less, require less floor space, and have somewhat higher efficiency.

The windings of either core-type or shell-type three-phase transformers may be connected in either wye or delta. Four possible combinations of connections for the three-phase, two- winding transformers are Y- Δ, Δ -Y, Δ -Δ , and Y-Y. These are shown in Figure with the transformers assumed to be ideal. The windings on the left are the primaries, those on the right are the secondaries, and a primary winding of the transformer is linked magnetically with the secondary winding drawn parallel to it. With the per-phase primary-to-secondary turns ratio (N1/N2 = a), the resultant voltages and currents for balanced applied line-to-line voltages V and line currents I are marked in the figure.

2459_Explain working of three-phase transformers.png

As in the case of three-phase circuits under balanced conditions, only one phase needs to be considered for circuit computations, because the conditions in the other two phases are the same except for the phase displacements associated with a three-phase system. It is usually convenient to carry out the analysis on a per-phase-of-Y (i.e., line-to-neutral) basis, and in such a case the transformer series impedance can then be added in series with the transmission-line series impedance. In dealing with Y- Δ and Δ -Y connections, all quantities can be referred to the Y-connected side. For Δ- Δ connections, it is convenient to replace the -connected series impedances of the transformers with equivalent Y-connected impedances by using the relation.

2044_Explain working of three-phase transformers1.png

It can be shown that to transfer the ohmic value of impedance from the voltage level on one side of a three-phase transformer to the voltage level on the other side, the multiplying factor is the square of the ratio of line-to-line voltages, regardless of whether the transformer connection is Y-Y, Δ -Y, or Δ -Δ . In some cases, where Y-Y transformation is utilized in particular, it is quite common to incorporate a third winding, known as tertiary winding, connected in delta. Such multiwinding transformers with three or more windings are not considered in this text.


Related Discussions:- Explain working of three-phase transformers

Write notes on clamping, Q. Write notes on clamping ? Clamping network ...

Q. Write notes on clamping ? Clamping network shifts (clamps) a signal to a different d.c level, that is it introduces a d.c. level to an a.c signal. Hence, the clamping networ

What is an opcode, What is an Opcode? The part of the instruction that ...

What is an Opcode? The part of the instruction that specifies the operation to be performed is known as the operation code or opcode

Evaluate supply and the supply power factor, Q. Two balanced, three-phase, ...

Q. Two balanced, three-phase, wye-connected loads are in parallel across a balanced three-phase supply. Load 1 draws a current of 20 A at 0.8 power factor leading, and load 2 draws

Metal oxide field effect transistor, Metal Oxide Field Effect Transistor ...

Metal Oxide Field Effect Transistor The metal-oxide-semiconductor field-effect transistor (MOSFET/MOS-FET/MOS FET) is a device employed for amplifying or for switching electr

Define power-supply rejection ratio, Q. Define Power-Supply Rejection Ratio...

Q. Define Power-Supply Rejection Ratio? An op amp's ability to disregard changes in power-supply voltage is measured by the power- supply rejection ratio (PSRR), which is speci

Efficiency of shunt geranerator, A 100kw,230v,dc shunt generator,with Ra=0....

A 100kw,230v,dc shunt generator,with Ra=0.05,and Rf=57.5 has no load rotational loss(friction,wandage,core loss)of 1.8kw.compute a) The generator efficiency at full load.

DC motor and DC generator, write down the similarities between motors and g...

write down the similarities between motors and generators

Combinational logic circuit , Design a combinational logic circuit to conve...

Design a combinational logic circuit to convert XS3BCD code in to the  standard 8421 BCD code.

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd