Q. A 10-kVA, 200:400-V, single-phase transformer gave these test results:

• Open-circuit test (LVwinding supplied): 200V, 3.2 A, 450 W

• Short-circuit test (HV winding supplied): 38 V, 25 A, 600 W

Compute the efficiency when the transformer delivers half its rated kVA at 0.85 power factor lagging.


Related Discussions:- Compute efficiency of transformer in power factor lagging

Induction motor, This is a synchronous motor that does not require a specia...

This is a synchronous motor that does not require a special start-up auxiliary motor. The  rotor  consists  of  stout  copper  (or aluminium)  conductors  arranged  in  the form of

Illustrate bcd-to-decimal decoding, Q. Illustrate BCD-to-decimal decoding w...

Q. Illustrate BCD-to-decimal decoding with a 4-to- 16 decoder, and draw the corresponding truth table.

Kpi for second stage implementation, KPI for Second Stage Implementation ...

KPI for Second Stage Implementation These KPIs deal along with the quality of the relationship among a supplier and a user (customer). They are significant to potential custom

Charge variation with time, Q. A charge variation with time is given in Fig...

Q. A charge variation with time is given in Figure. Draw the corresponding current variation with time.

Principle of oscillation in an rc phase shift oscillator, Q. What is the ba...

Q. What is the basic principle of oscillation in an RC phase shift oscillator. With a neat sketch explain its working? For producing oscillations there must have positive feedb

Requirement for an intrinsically safe circuit, Compute the ampacity of a 25...

Compute the ampacity of a 250 AWG copper conductor with type UF insulation that will be used in an area with an ambient temperature of 79°F (26°C). State the ampacity and explain h

Force between current carrying conductors, If a second current carrying con...

If a second current carrying conductor is placed near to the first and the corresponding magnetic fields drawn, we can begin to visualise why a force is created between them. If

Explain relative data addressing mode, Explain relative data addressing mod...

Explain relative data addressing mode (with examples) available in microprocessors. Relative Mode: Operand supplied is an offset, not the actual address. Added the con

permanent magnet stepper motor - stepper motor , Normal 0 fa...

Normal 0 false false false EN-IN X-NONE X-NONE   Permanent   Magnet Stepper Motor The s

Write Your Message!

Captcha
Free Assignment Quote

Assured A++ Grade

Get guaranteed satisfaction & time on delivery in every assignment order you paid with us! We ensure premium quality solution document along with free turntin report!

All rights reserved! Copyrights ©2019-2020 ExpertsMind IT Educational Pvt Ltd