Test schedule - meter testing, Electrical Engineering

Test Schedule - Meter Testing

The test schedule as per the Central Electricity Authority Regulations on Installation and Operation of Meters is given below.

Table: Test Schedule

Meter Type

Schedule

Single Phase LT meters

Once in 5 years after installation

LT three phase meters (CT operated) 20 kVA to 100 kVA

Once in a year to be checked since these are installed for high value consumers

Other LT metering systems

Once in two years after installation

EHT / HT meters

Below 5 MVA - Once in a year
5 to 10 MVA - Once in six months
above 10 MVA - Once in a quarter

The testing schedule for HT consumers should cover the whole Metering System involving CTs, PTs and Pilot Wire. Detailed ratio testing of CT, PT and control Pilot/ wires is to be completed. Testing by mobile vans/mobile cubicles through secondary injections kit and phantom loading might also be carried out through Measurement Unit. All new meters should meet the needs of Accuracy Class spelt out in Table.

                                                   Table: Requirements of Accuracy Class

Type of Consumer

Overall Accuracy Class

EHT Consumers (33 kV)

0.2

HT Consumer (44 to 33 kV)

0.5 or better

LT Consumer (Whole Current meters)

1.0 or better

LT Consumers (CT operated)

1.0 or better

 

Posted Date: 2/6/2013 7:54:37 AM | Location : United States







Related Discussions:- Test schedule - meter testing, Assignment Help, Ask Question on Test schedule - meter testing, Get Answer, Expert's Help, Test schedule - meter testing Discussions

Write discussion on Test schedule - meter testing
Your posts are moderated
Related Questions
Its not essential that a power plant uses only two rectifiers, it depends on the load there at the site and the capacity of the rectifier or SMPS. Assume the load at the site is 12

Q. The dual situations is shown in Figure , in which a high-pass and a low-pass filter are connected in parallel to produce a bandstop filter. With ω CLP = 10 CHP = 50, ω 0

How can I get an oscillator to genarate a sinusoid instead of a triangle wave

Q. Explain crossbar exchange, with all call processing steps and diagrams. Ans: The basic concept of crossbar switching is to provide a matrix of n x m sets of contacts with

Q A12-V, 115-Ah automobile storage battery is used to light a 6-W bulb. Assuming the battery to be a constant-voltage source, find how long the bulb can be lighted before the batte

Q. Explain working of Public Switched Telephone Network? Public Switched Telephone Network (PSTN) accommodates two kinds of subscribers: private andpublic. Subscribers to priv

Gaussian derivatives Generate Gaussian kernels for a given scale "sigma", and display the kernel. The size of the kernel should be floor(3*sigm)+1; (i) Write an m-file "

diagram of static generators

Q. Consider the synchronous counter shown in Figure of the text. (a) Draw its timing diagram. (b) Show the implementation of the same synchronous counter using D flip-flops.

A 200-V dc shunt motor has a field resistance of 200  and an armature resistance of 0.5 . On no load, the machine operates with full field flux at a speed of 1000 r/min with an a