Technical loss in electrical systems, Electrical Engineering

Technical Loss in Electrical Systems

Technical loss is inherent in electrical systems, as all electrical devices have a few resistances and the flow of currents causes a power loss (I2R loss). Integration of this power loss over time, i.e. ∫ I2R.dt is the energy loss. Every element in a power system (a line or a transformer) offers resistance to power flow and, therefore, consumes some energy although performing the duty expected of it. The cumulative energy consumed by all these elements is classified as "Technical Loss." Technical losses are because of energy dissipated in the conductors and equipment used for Transmission, Transformation, Sub- transmission and Distribution of Power. These occur at several places in a distribution system - in lines, mid-span joints and terminations transformers, service cables and connections and etc.

Table: Losses Due to Technical Reasons

•  Line losses

•  Loss in conductors/cables where lowersize conductors are used. This causessags and temperature rise in conductorswhich further aggravate the loss,

•  Loss in higher loaded phase wires due to unbalanced loading,

•  Loss due to current in neutral for cases or unbalance where neutral wires of lowersize are used (like 3 ½ core cables, andneutral wires of size lower than phasewires),

•  Loosening of strands (in multi-strandconductors like ACSR, AAC, AAA, etc.). 

•  Loss in mid-span joints

(or any joint) and at

terminations

•  Contacts of joints due to improper installation and looseness,

•  Contacts of joints due to inadequatesurface area of contact.

•  Loss in transformers

(typically DTs)

 

•  Loose connections at bushings,

•  Bend in jumpers at connectors where the strands are not tightly held,

•  High no-load loss depending on type of core used, 

•  High no-load loss in repaired transformers where the core has not been properly tightened,

•  No load loss in case a large number of lightly loaded DTs,

•  High copper loss for transformers operating at sub-optimal loading which is not commensurate with the designed optimal loading. 

•  Loss in service cables

and connections

•  Undersized service cables,

•  Loss in joints of service cables at the poles/junction boxes,

•  Use of inappropriate fasteners without spring washers at the crimped joints.

•  Loss due to high

impedance faults

•  Tree touching, creepers, bird nesting,

•  Insulator breakages and tracking on surface of the insulator.

•  Loss in re-wired

fuses/jumpers

•  Loose connections,

•  Inadequate size of fuse wires - often a source of hot spots.

The magnitude of energy dissipation depends hugely on the pattern of loading of transmission and distribution lines, kinds of loads, design of lines and etc. It is not probable to eliminate such losses inherent in a system altogether. They could, thus, be reduced to some extent. The technical losses could be further sub-grouped depending upon the stage of power transformation and transmission system as Sub-transmission losses (33 kV/11kV), Transmission losses (400 kV/220 kV/132 kV/66 kV), and Distribution losses (11 kV/0.4 kV).

Posted Date: 2/6/2013 4:22:59 AM | Location : United States







Related Discussions:- Technical loss in electrical systems, Assignment Help, Ask Question on Technical loss in electrical systems, Get Answer, Expert's Help, Technical loss in electrical systems Discussions

Write discussion on Technical loss in electrical systems
Your posts are moderated
Related Questions
What is memory mapping? The assignment of memory addresses to several registers in a memory chip is known as memory mapping.

can you help with my electronic principle assignment

Q. A wye-connected, three-phase, 50-Hz, six-pole synchronous alternator develops a voltage of 1000 V rms between the lines when the rotor dc field current is 3A. If this alternator

hi there i just need help for Electrical Engineering Design Report about any topic (prefer charger and inverter) which should be include Summary,Table of contents,Introduction,Body

a train weight 5 megaN is taking a slope of 1 in 200 at 45 kmper hour.the engine put in 100 kw.determine the power to be put in by the engine it the train take the slope up of 1 in

Configured dual processor architecture  In centralized SPC, dual processor architecture can be configured to operate in following one of three modes: 1.  Standby mode: In

what is the advantage and disadvantage of back to back test of transformer

A battery having of 12 cells are divided in three group which each group having of four cells in series. The three groups are joined in parallel. The emf of every cell is 1.5V and

A 3 phase 60 hertz induction motor has 8 poles and operates with a slip of .05 for a certain load. Compute in r.p.m. the (a) Speed of the rotor with respect to the stator, (b

Q. Basic Operation of  P-channel enhancement MOSFET? In the fabrication of a p-channel depletion field-effect transistor, the gate is insulated from the channel. Therefore, the