Technical loss in electrical systems, Electrical Engineering

Technical Loss in Electrical Systems

Technical loss is inherent in electrical systems, as all electrical devices have a few resistances and the flow of currents causes a power loss (I2R loss). Integration of this power loss over time, i.e. ∫ I2R.dt is the energy loss. Every element in a power system (a line or a transformer) offers resistance to power flow and, therefore, consumes some energy although performing the duty expected of it. The cumulative energy consumed by all these elements is classified as "Technical Loss." Technical losses are because of energy dissipated in the conductors and equipment used for Transmission, Transformation, Sub- transmission and Distribution of Power. These occur at several places in a distribution system - in lines, mid-span joints and terminations transformers, service cables and connections and etc.

Table: Losses Due to Technical Reasons

•  Line losses

•  Loss in conductors/cables where lowersize conductors are used. This causessags and temperature rise in conductorswhich further aggravate the loss,

•  Loss in higher loaded phase wires due to unbalanced loading,

•  Loss due to current in neutral for cases or unbalance where neutral wires of lowersize are used (like 3 ½ core cables, andneutral wires of size lower than phasewires),

•  Loosening of strands (in multi-strandconductors like ACSR, AAC, AAA, etc.). 

•  Loss in mid-span joints

(or any joint) and at

terminations

•  Contacts of joints due to improper installation and looseness,

•  Contacts of joints due to inadequatesurface area of contact.

•  Loss in transformers

(typically DTs)

 

•  Loose connections at bushings,

•  Bend in jumpers at connectors where the strands are not tightly held,

•  High no-load loss depending on type of core used, 

•  High no-load loss in repaired transformers where the core has not been properly tightened,

•  No load loss in case a large number of lightly loaded DTs,

•  High copper loss for transformers operating at sub-optimal loading which is not commensurate with the designed optimal loading. 

•  Loss in service cables

and connections

•  Undersized service cables,

•  Loss in joints of service cables at the poles/junction boxes,

•  Use of inappropriate fasteners without spring washers at the crimped joints.

•  Loss due to high

impedance faults

•  Tree touching, creepers, bird nesting,

•  Insulator breakages and tracking on surface of the insulator.

•  Loss in re-wired

fuses/jumpers

•  Loose connections,

•  Inadequate size of fuse wires - often a source of hot spots.

The magnitude of energy dissipation depends hugely on the pattern of loading of transmission and distribution lines, kinds of loads, design of lines and etc. It is not probable to eliminate such losses inherent in a system altogether. They could, thus, be reduced to some extent. The technical losses could be further sub-grouped depending upon the stage of power transformation and transmission system as Sub-transmission losses (33 kV/11kV), Transmission losses (400 kV/220 kV/132 kV/66 kV), and Distribution losses (11 kV/0.4 kV).

Posted Date: 2/6/2013 4:22:59 AM | Location : United States







Related Discussions:- Technical loss in electrical systems, Assignment Help, Ask Question on Technical loss in electrical systems, Get Answer, Expert's Help, Technical loss in electrical systems Discussions

Write discussion on Technical loss in electrical systems
Your posts are moderated
Related Questions
Q. Current-carrying conductors? Current-carrying conductors, when placed in magnetic fields, experience mechanical force. Considering only the effect of the magnetic field, the

Discuss DMA operation in brief. The fundamental idea of DMA is to transfer blocks of data directly among memory and peripherals. The data don't suffer the microprocessor but th

The    French    scientist,    Ampere,    (1775- 1836), conducted a series of experiments on the force between current carrying conductors. He found that: force per metre of wire (

The resistance of a 5 m length of wire is 600Ω.Determine: a)  the resistance of an 8 m length of the same wire, b)  the length of the same wire when the resistance is 420Ω

Q. Draw a 100 line exchange using two motion selectors and elucidate, how switching takes place in it. Ans: In a 100 line exchange, every subscriber is assigned a 2 digit

Q. A 230-Vdc shuntmotor delivers 30 hp at the shaft at 1120 r/min. If the motor has an efficiency of 87% at this load, find: (a) The total input power. (b) The line current.

Q. Explain common collector configuration? It is called the common-collector configuration because (ignoring the power supply battery) both the signal source and the load share

Q. What is Output Impedance? Output Impedance : The output impedance of an amplifier is a measure of the impedance or resistance. It has nothing to do with the actual loading t

Q. What are the different types of distributing frames used in exchanges? Ans: Different distribution  frames  used  in  exchange  are  displayed in  figure.  Each subscribe

Q. A rigid 50- coaxial transmission line has air as dielectric. If the radius of the outer conductor is 1 cm, find the cutoff frequency