New assembly buildings - fire protection engineering, Other Engineering

New Assembly Buildings:

12.1.1.1 The requirements of this chapter shall apply to new buildings or portions thereof used as an assembly occupancy.

12.1.3.2 Simultaneous Occupancy. Exits shall be sufficient for simultaneous occupancy of both the assembly occupancy and other parts of the building, except where the

authority having jurisdiction determines that the conditions are such that simultaneous occupancy will not occur.

12.1.6 Minimum Construction Requirements. Assembly occupancies shall be limited to

the building construction types specified in Table 12.1.6, based on the number of stories in height as defined in 4.6.3, unless otherwise permitted by the following: (1) This requirement shall not apply to outdoor grandstands of Type I or Type II construction.

(2) This requirement shall not apply to outdoor grandstands of Type III, Type IV, or

Type V construction that meet the requirements of 12.4.8.

(3) This requirement shall not apply to grandstands of non-combustible construction supported by the floor in a building meeting the construction requirements of Table

12.1.6.

(4) This requirement shall not apply to assembly occupancies within mall buildings in accordance with 36.4.4.

12.1.7.1 General. The occupant load, in number of persons for whom means of egress

and other provisions are required, shall be determined on the basis of the occupant load factors of Table 7.3.1.2 that are characteristic of the use of the space or shall be determined as the maximum probable population of the space under consideration, whichever is greater.

12.1.7.1.1 In areas not in excess of 930 m2, the occupant load shall not exceed one person in 0.46 m2.

12.1.7.1.2 In areas in excess of 930 m2, the occupant load shall not exceed one person in 0.65 m2.

12.1.7.2 Waiting Spaces. In theaters and other assembly occupancies where persons are admitted to the building at times when seats are not available, or when the

permitted occupant load has been reached based on 12.1.7.1 and persons are allowed to wait in a lobby or similar space until seats or space is available, all of the following

requirements shall apply:

(1) Such use of a lobby or similar space shall not encroach upon the required clear width of exits.

(2) The waiting spaces shall be restricted to areas other than the required means of egress.

(3) Exits shall be provided for the waiting spaces on the basis of one person for each 0.28 m2 of waiting space area.

 

Posted Date: 10/22/2012 6:08:48 AM | Location : United States







Related Discussions:- New assembly buildings - fire protection engineering, Assignment Help, Ask Question on New assembly buildings - fire protection engineering, Get Answer, Expert's Help, New assembly buildings - fire protection engineering Discussions

Write discussion on New assembly buildings - fire protection engineering
Your posts are moderated
Related Questions
Liquidity Ratios: The liquidity ratios of the company help in determining the ability of the company to convert its current or liquid assets readily into cash. Higher the ratios be



APPLICATION TO THE AXIAL FLOW COMPRESSOR: In order for the compressor to deliver a high mass airflow for a minimum effort required to drive it, it is important that all the com

Exhaust Jet Mixing: Figure shows that the noise from the exhaust jet is the main contributor to the total noise generated by a low by-pass ratio turbo-fan. For a turbo-jet the

Engineers sometimes add chlorine to pipes to disinfect water. It is desired to achieve four logs of kill. This means that the effluent concentration of microoganisms is 10^-4 times

What is Variable Interest Rate? Interest rates which is offered by banks or financial institutions on loans or deposits which are liable to change according to circumstances. For e

WHY VOLTAGE GENERATED IN MULTIPLES OF 11

Expertsmind.com brings you unique solution in electrical engineering Class A Amplifier Operation Class A amplifiers are biased so that variations in input signal polarit

Comparison of FP result with experiment At the lowest test lift coefficient the flow is just subcritical (in the sense that the Mach number of the flow component normal to the