3) The impedance for a 120 km, 230-kV line is given as j 0.9 ohm/km and
j 0.6 ohm/km for self and mutual terms respectively; resistance is neglected. The mho
characteristic for the line’s distance protection is set to reach 100 km at the line’s
characteristic impedance angle. Assume that a line-to-ground fault occurs at a distance “x”
from the relay by contact with a tree branch, where the tree presents an impedance of 30
ohms to the flow of fault current.
(a) What is the impedance seen by the relay, expressed as a function of x?
(b) What is the relay reach (in km) for this fault condition (i.e. at what distance from the relay
is the fault on the verge of going undetected)?
Posted Date: 4/2/2013 3:39:00 PM | Location :







Related Discussions:- Impedance / DUTT, Assignment Help, Ask Question on Impedance / DUTT, Get Answer, Expert's Help, Impedance / DUTT Discussions

Write discussion on Impedance / DUTT
Your posts are moderated
Related Questions
Athree-phase, 440-V, 60-Hz, four-pole induction motor operates at a slip of 0.025 at full load, with its rotor circuit short-circuited. This motor is to be operated on a 50-Hz supp

Q. In the Wheatstone bridge circuit shown in Figure, R 1 = 16, R 2 = 8, and R 3 = 40; R 4 is the unknown resistance. RM is the galvanometer resistance of 6 . If no current

Discuss the DWORD assembler directive with example. DWORD: This defines word type variable. The described variable may have one or more initial values into the dire

does wein bridge can be used for frequency measurement? how it is possible?

Write an Assembly language program that will produce a PWM signal with a desired average voltage. The user selects the desired average voltage by pressing keys 1 - 4. If the

1) only one pair of slip rings are required (to energise the rotating field coil) regardless of the number of phases produced by the alternator (three phases is common because of t


Two single-phase 60-Hz sinusoidal-source generators (with negligible internal impedances) are supplying to a common load of 10 kW at 0.8 power factor lagging. The impedance of the


hi can you help me to create a dc to 3 phase ac circuit which can exceed at any point: 50V and 20A and 400W maximum. The output should be variable from about 0 – 25V per phase, wi