Determine ratio between mass flow rate to condensing steam, Mechanical Engineering

Determine ratio between mass flow rate to condensing steam:

In steam power plant, the steam 0.1 bar and 0.95 dry enters condenser and leaves as saturated liquid at 0.1 bar and 45°C. Cooling water enters condenser in separate steam at 20°C and leaves at 35°C without any loss of its pressure and with no phase change. Neglecting heat interaction between condenser and surroundings and changes in kinetic energy and potential energy, determine ratio between mass flow rate of cooling water to condensing steam.              

Sol.: Given that:

Inlet condition of steam: Pressure 'P1' = 0.1 bar dryness fraction x = 0.95 The exit condition of steam saturated water at 0.1 bar and 45°C Inlet temperature of cooling water = 20°C Exit temperature of cooling water = 35°C Applying SFEE to control volume Q - Ws  = mf [(h2  - h1)+  ½(V22 - V12) + g(z2 - z1)]

1991_Determine ratio between mass flow rate to condensing steam.png

Figure

neglecting changes in kinetic and potential energies. And there is no shaft work that is.; Ws  = 0

Q = mf (h2  - h1)

h1 = hf1  + xhfg1

= 191.81 + 0.95 (2392.82) = 2464.99 kJ/kg

h2 = hf2  at 0. 1 bar (as the water is saturated liquid)

h2 = 191.81 kJ/kg

Q = mf (191.81 - 2464.99)

= - 2273.18mf  kJ/kg                              ...(i)

negative sign shows the heat rejection.

 

1973_Determine ratio between mass flow rate to condensing steam1.png

By energy balance; Heat lost by steam = Heat gained by cooling water

Q = mfw.Cw  (T4  - T3) = mfw  x 4.1868(35 - 20) = 62.802mf                ...(ii)

Equate equation (i) and (ii); We get Q = -2273.18mf  = 62.802mfwmfw/m = 36.19 Ratio of mass flow rate of cooling water to the condensing steam = mfw/mf  = 36.19                                                                      

Posted Date: 10/15/2012 8:02:15 AM | Location : United States







Related Discussions:- Determine ratio between mass flow rate to condensing steam, Assignment Help, Ask Question on Determine ratio between mass flow rate to condensing steam, Get Answer, Expert's Help, Determine ratio between mass flow rate to condensing steam Discussions

Write discussion on Determine ratio between mass flow rate to condensing steam
Your posts are moderated
Related Questions
Torque of Multiple and Different Sized Fasteners: First tighten all fasteners by the help of free hand. Then torque big fasteners first followed by torque of smaller fasteners in

A hermite curve passes through the points (1,0), (0.866, 0.5), (0.5, 0.866), (0,1) which are parameterized at u=0,0.25,0.75,1 respectively. determine geometric coefficient of the c

Process capability Process capability which is a measurement with respect to the inherent precision of a manufacturing process has two significant elements, i.e. process facto

Carno t Theorem: No heat engine operating in cycle between the two given thermal reservoir, having fixed temperature can be more efficient than reversible engine operating be

(a) Derive an expression for the otto cycle to determine the Mean Effective Pressure and efficiency. (b)The two engines are to perform on diesel and otto cycle with the followin

Find out the modulus of elasticity: A unidirectional FRP is produced with fibre volume ratio of 60%. The density of fibre is 1480 kg/m 3 and that of matrix is 1200 kg/m 3 . C

Q. Analog Control System for steam generator ? The analog (modulating) control of the Steam Generators will be performed using a Process Control System (by Buyer). Detailed fun

A Mercedes-Benz 300SL (m = 1600 kg) is parked on a road that rises 20° above the horizontal. (a) What is the static frictional force that the ground exerts on the tires? (b) Wh

Determine moment of this normal force - rectangular beam: A rectangular beam contains a width of 100 mm and a depth of 200 mm. This is utilized as a simply supported beam & th