Determine ratio between mass flow rate to condensing steam, Mechanical Engineering

Determine ratio between mass flow rate to condensing steam:

In steam power plant, the steam 0.1 bar and 0.95 dry enters condenser and leaves as saturated liquid at 0.1 bar and 45°C. Cooling water enters condenser in separate steam at 20°C and leaves at 35°C without any loss of its pressure and with no phase change. Neglecting heat interaction between condenser and surroundings and changes in kinetic energy and potential energy, determine ratio between mass flow rate of cooling water to condensing steam.              

Sol.: Given that:

Inlet condition of steam: Pressure 'P1' = 0.1 bar dryness fraction x = 0.95 The exit condition of steam saturated water at 0.1 bar and 45°C Inlet temperature of cooling water = 20°C Exit temperature of cooling water = 35°C Applying SFEE to control volume Q - Ws  = mf [(h2  - h1)+  ½(V22 - V12) + g(z2 - z1)]

1991_Determine ratio between mass flow rate to condensing steam.png

Figure

neglecting changes in kinetic and potential energies. And there is no shaft work that is.; Ws  = 0

Q = mf (h2  - h1)

h1 = hf1  + xhfg1

= 191.81 + 0.95 (2392.82) = 2464.99 kJ/kg

h2 = hf2  at 0. 1 bar (as the water is saturated liquid)

h2 = 191.81 kJ/kg

Q = mf (191.81 - 2464.99)

= - 2273.18mf  kJ/kg                              ...(i)

negative sign shows the heat rejection.

 

1973_Determine ratio between mass flow rate to condensing steam1.png

By energy balance; Heat lost by steam = Heat gained by cooling water

Q = mfw.Cw  (T4  - T3) = mfw  x 4.1868(35 - 20) = 62.802mf                ...(ii)

Equate equation (i) and (ii); We get Q = -2273.18mf  = 62.802mfwmfw/m = 36.19 Ratio of mass flow rate of cooling water to the condensing steam = mfw/mf  = 36.19                                                                      

Posted Date: 10/15/2012 8:02:15 AM | Location : United States







Related Discussions:- Determine ratio between mass flow rate to condensing steam, Assignment Help, Ask Question on Determine ratio between mass flow rate to condensing steam, Get Answer, Expert's Help, Determine ratio between mass flow rate to condensing steam Discussions

Write discussion on Determine ratio between mass flow rate to condensing steam
Your posts are moderated
Related Questions
Different types of information units of CAD There are different types of information units defined. They are : Class 0 The geometric primitives needed for describing 2- a

how i make assigment for newton s ring

corrosion in boilers is prevented or minimized by maintaining of boiler water


Open belt drive: An open belt drive connects the two pulleys 120cm and 50cm diameter on parallel shafts which are apart 4m. The maximum tension in belt is 1855.3N. Coefficien

Derive a regression forecasting equation: The general manager of a company producing road rollers is convinced that the demand for road rollers is associated to the number of


Velocity acquired by block - system released from rest: T wo blocks shown in the figure given below, have masses A = 20N and B = 10N and the coefficient of friction between

I have faced a serious problem of Lead segregation and porosity in Copper Tin Zn alloy containing 26-30 % lead sand castings.Can anybody throw light on this

yuuiiopp